superholz wrote:... I would like to understand what is the technical difficulty that causes that the TRV controller misses the wake up. Furhter just curious: what happens onder the hood of you plugin when the heating is switched off. In other words, which variable/property you use to decide that the setpoint is reached?
It is not a problem with the TRV Controller. It is just letting you know that the controlled TRV hasn't woken up as it should do according to its wakeup time set in its device settings.
This can happen regardless as to whether the TRV is being controlled or not. It is just that the TRV Controller is monitoring the wakeups and can therefore tell you that one has been missed.
You likely wouldn't know otherwise because Indigo doesn't warn you that it is happening.
The significance is that if for example you have a 15 minute wakeup period , then to make sure that the heating is on at 17:00, you would have to turn on the heating (i.e set the setpoint) at 16:45 just in case a wakeup happens at 16:58 in which case the next wakeup is 17:13. If this wakeup was missed then the next one is 17:28 which is almost half an hour late.
What wakeup period have you set for your TRV?
The plugin will switch off the TRV (set to minimum setpoint) once the measured temperature from the Remote (if defined) or TRV is reached. So the property is the measured temperature. This is shown in the Indigo UI and also in the custom states.