Inconsistent behaviour
Mon Jan 04, 2021 5:38 am
siclark offline
Hi Jon, Might be missing something there, but these 2 rooms seem to be behaving differently
Screenshot 2021-01-04 at 11.28.53.png (42.82 KiB) Viewed 3881 times
At approx 15:00 the temp sensor goes above the Stat SP and the TRV SP is set to 8 c from its overriden value 3 degrees above the Stat SP and the valve goes off.
However on this one
Screenshot 2021-01-04 at 11.36.20.png (50.07 KiB) Viewed 3881 times
The plug in doesnt seem to adjust the TRV SP to 8 and so it continues to manage the temperature to the overriden TRV SP using the valve % so the room maintains at a higher temperature than the desired set point.
Both use remote temperature sensors and appear to have the same settings.
Any ideas?
Simon
Mon Jan 04, 2021 7:55 am
autolog offline
Re: Inconsistent behaviour
Hi Simon.
Happy New Year to you. :D
Looking at the second image, both the Remote and TRV set-points seem to be going to 8C between 14:00 and 17:00?
So unless I am missing something, it looks OK?
Mon Jan 04, 2021 7:59 am
siclark offline
Happy new year to you too.
It’s at 18:00 where I’d expect the TRV set point to go to 8 as the room temp was higher than the desired set point
Mon Jan 04, 2021 8:12 am
autolog offline
I agree, it doesn't seem correct. :(
Are you sure that the Remote Stat is being used to monitor the temperature? I know you probably are, but just double checking.
Because, if it was using the TRV temperature to monitor the temp, it would be correct.
Wed Nov 10, 2021 3:05 am
siclark offline
Hi Jon. Its that time of year again and realised that this strange behaviour is still happening on the twins' thermostat.
Its not setting the setpoint on the TRV to 8 once the remote temperature reaches the plugin setpoint of 20.
Any ideas what might be going wrong?
Screenshot 2021-11-10 at 09.03.18.png (402.74 KiB) Viewed 3392 times
Screenshot 2021-11-10 at 09.03.05.png (441.63 KiB) Viewed 3392 times
Screenshot 2021-11-10 at 08.59.15.png (51.82 KiB) Viewed 3392 times
Wed Nov 10, 2021 3:48 am
siclark offline
Interestingly I was getting this behaviour on another room and created a new TRV controller device with what I thought were same settings, moved all the dependencies over and deleted the original device.
The behaviour is now as expected, ie the TRV setpoint goes to 8 when the remote temperature sensor is higher than the controller setpoint.
Is it possible that the old device has not properly captured the remote sensor despite it showing in the GUI?
Wed Nov 10, 2021 9:02 am
autolog offline
Hi Simon,
I agree it looks odd. :?
Is there anything special about the Twin Temp piBeacon and is that the same stat in other room that is working OK?
You could try the procedure you use in the other room to correct it on the twins' room, to see if that resolves it.
Other than that, I would probably need to see some debugging logs for the time period it happens in order to see if that throws any light on the issue?
Wed Nov 10, 2021 10:58 am
siclark offline
Yes I’ve recreated a trv controller device. Copied settings from the screenshots on here and deleted the old one. Initial impressions are that it now work as expected whereas the old one didn’t.
Thu Nov 11, 2021 1:31 pm
siclark offline
I have turned on debugging on the plugin and will try some tests this evening. One of the rooms where I recreated a new device is still not setting the TRV SP back to 8 so will try and capture an event to share.
Thu Nov 11, 2021 5:31 pm
siclark offline
I set the trv controller to 21 at 19:20 and it did some weird behaviour. The TRV isnt 5 degrees higher and the the TRV is not set to 8 when the remote temp exceeds the set point.
Screenshot 2021-11-11 at 23.22.19.png (74.33 KiB) Viewed 3291 times
Fri Nov 12, 2021 2:25 am
siclark offline
Morning Jon,
This is strange.. schedule set to set study to 21 with a 5 degree offset. Except the setpoint on the trv controller as well as the trv itself are both set to 26.
edit: when I reloaded the TRV plugin, the controller SP was reverted to 21 as it should be and the valve then went to off.
This seems to be the relevant bit of code. The setpointHeat was at 21 and setPointTRV at 26 for a second or 2, then the TRV seems to go to TRV hardware control and the setpointHeat goes to 26. There is a weird line with the setpoint at 119.8 at 08:00:17.348
==  Method: 'deviceUpdated'
==  Sequence: 78302
==  Device: TRV - 'Study TRV'
==  Last Communication: 2021-11-12 08:00:05
==  List of states to be queued for update by TRVHANDLER:
==    > Description = UPDATE ZWAVE EVENT SENT TRV, Value = 2021-11-12 08:00:17
==  Description of updates that will be performed by TRVHANDLER:
==    > TRV Z-Wave event sent. Time updated to '2021-11-12 08:00:17'. Sent count now totals: 158
2021-11-12 08:00:17.296   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [1] are: controllerMode = 1, setpointHeat = 21.0, setPointTrv =  26.0
2021-11-12 08:00:17.298   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [2] are: controllerMode = 1, setpointHeat = 21.0, setPointTrv =  26.0
2021-11-12 08:00:17.300   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [3] are: HVAC_FULL_POWER = False
2021-11-12 08:00:17.301   THREADDEBUG    Plugin.method.zwaveCommandReceived      Main Plugin Method
2021-11-12 08:00:17.301   THREADDEBUG    Plugin.method.controlTrvHeatingOn       TrvHandler Method
2021-11-12 08:00:17.304   DEBUG          Plugin.general.zwaveCommandReceived
ZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZZ
ZZ
ZZ  TRV Z-WAVE > RECEIVE INTERCEPTED: 01 0C 00 04 00 7F 06 31 05 01 42 06 9B 64 (node 127)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 12, Class = Sensor Multilevel, Verb = Verb 05, Temperature = 16.91
ZZ
2021-11-12 08:00:17.312   THREADDEBUG    Plugin.method.deviceUpdated             Main Plugin Method
2021-11-12 08:00:17.310   THREADDEBUG    Plugin.method.controlHeatingSource      TrvHandler Method
2021-11-12 08:00:17.320   DEBUG          Plugin.general.deviceUpdated             =======> RACE DETECTION FOR TRV 'Study TRV': SECONDS SINCE MIDNIGHT = '28817', COUNT = '4' [MAX = '8'] <=======
2021-11-12 08:00:17.326   DEBUG          Plugin.trvHandler.controlHeatingSource      Control Heating Source: Thermostats calling for heat from Variable 'HeatReqdHallway':
  > Dining Room Thermostat
  > Study Thermostat
2021-11-12 08:00:17.327   DEBUG          Plugin.general.deviceUpdated
==  Sequence: 78303
==    > Description = UPDATE ZWAVE EVENT RECEIVED TRV, Value = 2021-11-12 08:00:17
==    > TRV Z-Wave event received. Time updated to '2021-11-12 08:00:17'. Received count now totals: 165
2021-11-12 08:00:17.332   DEBUG          Plugin.trvHandler.run
TRVHANDLER: 'Study Thermostat' DEQUEUED COMMAND 'UPDATE TRV STATES'
2021-11-12 08:00:17.333   THREADDEBUG    Plugin.method.updateDeviceStates        TrvHandler Method
2021-11-12 08:00:17.339   DEBUG          Plugin.trvHandler.updateDeviceStates
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
XX  Method: 'updateDeviceStates'
XX  Sequence: 78301
XX  Device: TRV CONTROLLER - 'Study Thermostat'
XX  List of states to be updated:
XX    > Description = UPDATE ZWAVE EVENT RECEIVED TRV, Value = 2021-11-12 08:00:17
XX  States to be updated in the TRV Controller device:
XX    > {'value': '2021-11-12 08:00:17', 'key': 'zwaveEventReceivedDateTimeTrv'}
2021-11-12 08:00:17.339   THREADDEBUG    Plugin.method.zwaveCommandSent          Main Plugin Method
2021-11-12 08:00:17.339   THREADDEBUG    Plugin.method.controlTrv                TrvHandler Method
2021-11-12 08:00:17.348   DEBUG          Plugin.general.zwaveCommandSent
ZZ
ZZ  TRV Z-WAVE > SEND INTERCEPTED: 01 0A 00 13 7F 03 43 02 01 25 77 88 (node 127 ACK after 17 milliseconds)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 10, Class = Thermostat Setpoint, Verb = Get, Setpoint = 119.0
ZZ  'TRV' device Z-WAVE > Pending: True, Sequence:  '2', Setpoint: '26.0'
ZZ
2021-11-12 08:00:17.352   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' is set to Controller Mode 'TRV UI Control'
2021-11-12 08:00:17.353   THREADDEBUG    Plugin.method.deviceUpdated             Main Plugin Method
2021-11-12 08:00:17.355   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [1] are: controllerMode = 4, setpointHeat = 21.0, setPointTrv =  26.0
2021-11-12 08:00:17.360   DEBUG          Plugin.general.deviceUpdated             =======> RACE DETECTION FOR TRV 'Study TRV': SECONDS SINCE MIDNIGHT = '28817', COUNT = '5' [MAX = '8'] <=======
2021-11-12 08:00:17.363   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [2] are: controllerMode = 4, setpointHeat = 26.0, setPointTrv =  26.0
2021-11-12 08:00:17.365   DEBUG          Plugin.general.deviceUpdated
==  Sequence: 78304
==    > Description = UPDATE CONTROLLER MODE, Value = 4
==    > Controller Mode updated from Auto Schedule Control to TRV UI Control
==    > TRV Z-Wave event sent. Time updated to '2021-11-12 08:00:17'. Sent count now totals: 159
2021-11-12 08:00:17.368   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [3] are: HVAC_FULL_POWER = False
2021-11-12 08:00:17.369   THREADDEBUG    Plugin.method.controlTrvHeatingOn       TrvHandler Method
2021-11-12 08:00:17.382   THREADDEBUG    Plugin.method.controlHeatingSource      TrvHandler Method
2021-11-12 08:00:17.390   DEBUG          Plugin.trvHandler.controlHeatingSource      Control Heating Source: Thermostats calling for heat from Variable 'HeatReqdHallway':
  > Study Thermostat
2021-11-12 08:00:17.390   THREADDEBUG    Plugin.method.zwaveCommandReceived      Main Plugin Method
2021-11-12 08:00:17.395   DEBUG          Plugin.trvHandler.run
2021-11-12 08:00:17.402   DEBUG          Plugin.general.zwaveCommandReceived
ZZ
ZZ  TRV Z-WAVE > RECEIVE INTERCEPTED: 01 0C 00 04 00 7F 06 43 03 01 22 00 50 BD (node 127)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 12, Class = Thermostat Setpoint, Verb = Report, Setpoint = 8.0, Pending Controller Mode = TRV Hardware Control
ZZ
2021-11-12 08:00:17.402   THREADDEBUG    Plugin.method.updateDeviceStates        TrvHandler Method
2021-11-12 08:00:17.409   DEBUG          Plugin.trvHandler.updateDeviceStates
XX  Sequence: 78302
XX    > Description = UPDATE ZWAVE EVENT SENT TRV, Value = 2021-11-12 08:00:17
XX    > {'value': '2021-11-12 08:00:17', 'key': 'zwaveEventSentDateTimeTrv'}
2021-11-12 08:00:17.410   THREADDEBUG    Plugin.method.deviceUpdated             Main Plugin Method
2021-11-12 08:00:17.410   THREADDEBUG    Plugin.method.controlTrv                TrvHandler Method
2021-11-12 08:00:17.425   DEBUG          Plugin.general.deviceUpdated             =======> RACE DETECTION FOR TRV 'Study TRV': SECONDS SINCE MIDNIGHT = '28817', COUNT = '6' [MAX = '8'] <=======
2021-11-12 08:00:17.430   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' is set to Controller Mode 'TRV Hardware Control'
2021-11-12 08:00:17.432   DEBUG          Plugin.general.deviceUpdated
==  Sequence: 78305
==    > Description = UPDATE CONTROLLER MODE, Value = 3
==    > TRV Z-Wave event received. Time updated to '2021-11-12 08:00:17'. Received count now totals: 166
==    > Controller Mode updated from Auto Schedule Control to TRV Hardware Control
2021-11-12 08:00:17.435   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [1] are: controllerMode = 3, setpointHeat = 26.0, setPointTrv =  26.0
2021-11-12 08:00:17.438   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [2] are: controllerMode = 3, setpointHeat = 26.0, setPointTrv =  26.0
2021-11-12 08:00:17.438   THREADDEBUG    Plugin.method.zwaveCommandSent          Main Plugin Method
2021-11-12 08:00:17.441   DEBUG          Plugin.trvHandler.controlTrv                controlTrv: 'Study Thermostat' internal states [3] are: HVAC_FULL_POWER = False
2021-11-12 08:00:17.446   DEBUG          Plugin.general.zwaveCommandSent
ZZ
ZZ  TRV Z-WAVE > SEND INTERCEPTED: 01 09 00 13 7F 02 26 02 25 78 E1 (node 127 ACK after 7 milliseconds)
ZZ  TRV Z-WAVE > TRANSLATION: Name = 'Study TRV', Address = 127, Length = 9, Class = Switch Multilevel, Verb = Get, Get Valve Status
ZZ
Screenshot 2021-11-12 at 08.22.10.png (57.43 KiB) Viewed 3302 times
Screenshot 2021-11-12 at 08.24.29.png (369.33 KiB) Viewed 3302 times
Fri Nov 12, 2021 3:50 am
siclark offline
I have now started plotting the controllerMode in grafana and 2 of the TRV controllers are in mode 3, ie TRV Hardware Control, even though they havent been touched and have child lock on.
Restarting the plugin resets them to mode 0 Auto, but then they flip back to mode 3. Is this expected behaviour?
Fri Nov 12, 2021 11:54 am
autolog offline
Hi Simon,
Just catching up with posts. :)
I don't think it is expected behaviour? I would expect it to go into that mode if the setpoint was changed on the TRV.
I will investigate for you. The trouble is, when I have touched the code for ages, it takes a while to remind myself how it all works, or doesn't as the case may be. :wink:
EDIT:
What version of the plugin are you running to make sure that I am looking at the relevant version?
Fri Nov 12, 2021 12:32 pm
siclark offline
I did check with my wife that she didn’t touch the trv and in the other room I Was sat there the whole time.
The logging shows a lot of changing between modes on the 2 devices I recreated.
Fri Nov 12, 2021 1:44 pm
autolog offline
Yes, definitely looks odd; well spotted. :)
So, what version of the plugin are you running (you might have missed the edit on my previous post)?