Inovelli LZW31-SN dimmer not reporting correct state
Sat Jun 20, 2020 5:47 pm
edrabbit offline
I installed an Inovelli LZW31-SN dimmer switch to play with. I just updated to Indigo 7.4.1 to get it setup and things seem to be mostly working, except it's not always correctly reflecting the state of the light switch in Indigo. For example right now the light is off, but Indigo thinks it's on and at 100% brightness. If I click "Send Status Request" it corrects it. I can spend some time trying to figure out the exact steps to reproduce, but was wondering if anyone else had run into it and/or if it was a known issue before I spent more time doing that. My guess is that I'll need to set Status Polling to something more regular than "Only when activity detected" to keep things in sync and just deal with the increased ZWave traffic in my already noisy house.
Tue Jun 23, 2020 7:22 pm
Re: Inovelli LZW31-SN dimmer not reporting correct state
See what Z-Wave commands it is sending when you locally control it (at the switch). Turn on the Z-Wave Debug Logging checkbox (via the Interfaces->Z-Wave->Configure... menu item) first, then copy/paste the Event Log results into a reply for me. Also after locally controlling it, after say 10 seconds, send it a status request so I can see how it responds to that.
Mon Jun 29, 2020 10:00 am
brettlid offline
try excluding and then re-including the device. I've solved a similar issue with one of mine.
Mon Jun 29, 2020 9:43 pm
edrabbit offline
This is interesting, when I did that and watched Indigo it looks like it's actually getting the status but the status is reversed. i.e. If I turn on the switch locally, Indigo thinks the status should be off and vice versa. Got some logs for you:
   Z-Wave                          Indigo Device "064 - Dimmer Switch (LZW31-SN)" Z-Wave Properties:
Indigo Z-Wave Version: 7.4.1
Node ID: 64
Model: Dimmer Switch (LZW31-SN)
Model ID: 00010001
Manufacturer: Inovelli
Manufacturer ID: 031E
Protocol Version: 6.04
Application Version: 1.35
Model Definition Version: 3
Library Type: 3
Class Name: Dimmable Power Switch
Class Hierarchy: 04 : 11 : 01
Command Class Base: 26
Command Versions: 85v1 86v1 55v1 98v1 59v1 5Av1 5Bv1 5Ev1 9Fv1 20v1 22v1 26v2 27v1 6Cv1 72v1 70v1 32v3 73v1 75v1 7Av1
Features: routing, beaming, security, energyMeter
Neighbors: 5, 16, 17, 20, 34, 48
Associations: 1:[1] 2:[] 3:[] 4:[]
Config Values: 1:0 2:3 3:0 4:0 5:1 6:99 7:0 11:0 13:170 14:5 15:1 18:10 19:3600 20:10
   Z-Wave Debug                    stopping node healing thread
   Z-Wave Debug                    stopping node status polling thread
   Z-Wave Debug                    stopped zwave packet parser thread
   Z-Wave                          connection reset requested
   Z-Wave Debug                    starting serial connection loop
   Z-Wave Debug                    starting zwave packet parser thread
   Z-Wave Debug                    SENT getVersion: 01 03 00 15 E9
   Z-Wave Debug                    RCVD getVersion: 01 10 01 15 5A 2D 57 61 76 65 20 33 2E 39 35 00 01 99 (no inbound callback)
   Z-Wave Debug                    . .  getVersion: Z-Wave 3.95 static controller
   Z-Wave Debug                    SENT getHomeID: 01 03 00 20 DC
   Z-Wave Debug                    RCVD getHomeID: 01 08 01 20 F7 83 E3 1A 01 5A (no inbound callback)
   Z-Wave Debug                    . .  getHomeID: F783E31A, nodeID: 001
   Z-Wave Debug                    SENT getInterfaceFeatures: 01 03 00 05 F9
   Z-Wave Debug                    RCVD getInterfaceFeatures: 01 04 01 05 1C E3 (no inbound callback)
   Z-Wave Debug                    . .  getInterfaceFeatures: 1C
   Z-Wave Debug                    SENT getInterfaceApiCapabilities: 01 03 00 07 FB
   Z-Wave Debug                    RCVD getInterfaceApiCapabilities: 01 2B 01 07 01 00 00 86 01 01 00 5A FE 81 FF 88 4F 1F 00 00 FB 9F 7D A0 67 00 00 80 00 80 86 00 00 00 E8 73 00 00 0E 00 00 60 00 00 FA (no inbound callback)
   Z-Wave Debug                    . .  getInterfaceApiCapabilities: supportedFuncIDs: 02 03 04 05 06 07 08 09 10 11 12 13 14 15 16 17 18 1C 20 21 22 23 24 27 29 2A 2B 2C 2D 41 42 44 45 46 47 48 49 4A 4B 4C 4D 50 51 53 54 55 56 57 5E 60 61 62 63 66 67 80 90 92 93 98 B4 B6 B7 B8 B9 BA BD BE BF D2 D3 D4 EE EF
   Z-Wave Debug                    . .  getInterfaceApiCapabilities: serialApi 1.00, manufactureId 0086, productType 0101, productId 005A
   Z-Wave                          connected to Z-Stick Plus (ZW090) interface on /dev/cu.usbmodem411 (firmware 1.00)
   Z-Wave Debug                    SENT forceSUC: 01 05 00 54 01 01 AE
   Z-Wave Debug                    RCVD forceSUC: 01 04 01 54 01 AF (no inbound callback)
   Z-Wave Debug                    SENT getInitialNodeData: 01 03 00 02 FE
   Z-Wave Debug                    RCVD getInitialNodeData: 01 25 01 02 05 08 1D BB 8A DF 08 A2 F7 3D 9F 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 05 00 DD (no inbound callback)
   Z-Wave Debug                    . .  getInitialNodeData: is static update controller
   Z-Wave Debug                    . .  getInitialNodeData: [1, 2, 4, 5, 6, 8, 10, 12, 16, 17, 18, 19, 20, 21, 23, 24, 28, 34, 38, 40, 41, 42, 43, 45, 46, 47, 48, 49, 51, 52, 53, 54, 57, 58, 59, 60, 61, 64]
   Z-Wave Debug                    SENT getNodeProtocolInfo: 01 04 00 41 01 BB
   Z-Wave Debug                    RCVD getNodeProtocolInfo: 01 09 01 41 93 16 01 02 02 01 33 (no inbound callback)
   Z-Wave Debug                    . .  getNodeProtocolInfo:       node 001, class name: Static Computer Controller
   Z-Wave Debug                    . .  getNodeProtocolInfo:            class hierarchy: Static Controller : Static Controller : Static Computer Controller (02 : 02 : 01)
   Z-Wave Debug                    . .  getNodeProtocolInfo:         base class command: 00
   Z-Wave Debug                    . .  getNodeProtocolInfo:   supported class commands: 20
   Z-Wave Debug                    . .  getNodeProtocolInfo:     encrypt class commands:
   Z-Wave Debug                    . .  getNodeProtocolInfo:                   features: beaming
<Cut out a bunch of noise on other devices that didn't seem relevant>
   Z-Wave Debug                    SENT getNodeProtocolInfo: 01 04 00 41 40 FA
   Z-Wave Debug                    RCVD getNodeProtocolInfo: 01 09 01 41 D3 9C 01 04 11 01 EC (no inbound callback)
   Z-Wave Debug                    . .  getNodeProtocolInfo:       node 064, class name: Dimmable Power Switch
   Z-Wave Debug                    . .  getNodeProtocolInfo:            class hierarchy: Routing Slave : Mulitlevel Switch : Dimmable Power Switch (04 : 11 : 01)
   Z-Wave Debug                    . .  getNodeProtocolInfo:         base class command: 26
   Z-Wave Debug                    . .  getNodeProtocolInfo:   supported class commands: 20 26 27
   Z-Wave Debug                    . .  getNodeProtocolInfo:                   features: routing, beaming
   Z-Wave Debug                    starting node healing thread
   Z-Wave Debug                    starting node status polling thread
   Z-Wave Debug                    RCVD sensorSetLevel: 01 09 00 04 00 26 03 20 01 FF 09
   Z-Wave Debug                    . .  sensorSetLevel: node 038, endpoint None, cmdClass 20, value 255
   Z-Wave                          received "Master Bedroom (Motion)" status update is on
   Z-Wave Debug                    RCVD requestAlarmSensorStatus: 01 10 00 04 00 26 0A 71 05 00 00 00 FF 07 08 00 00 43
   Z-Wave Debug                    . .  requestAlarmSensorStatus: node 038, endpoint None, cmdClass 71, type 0, value 0, classSubKey 710000
   Z-Wave Debug                    . .  requestAlarmSensorStatus: typeExt 7, valueExt 8, classSubKeyExt 7100000708
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 04 0E 32 02 21 64 00 00 22 EC 00 C3 00 00 22 EC 53
   Z-Wave Debug                    . .  requestMeterLevel: node 004, endpoint None, meterType 01, raw value 6400...
   Z-Wave Debug                    . .  requestMeterLevel: 8.940 kWh (float: 8.940000)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 04 0E 32 02 21 74 00 00 00 00 00 C3 00 00 22 EC 8D
   Z-Wave Debug                    . .  requestMeterLevel: node 004, endpoint None, meterType 01, raw value 7400...
   Z-Wave Debug                    . .  requestMeterLevel: 0.000 W (float: 0.000000)
   Z-Wave Debug                    RCVD dimmerSetLevel: 01 09 00 04 00 40 03 20 03 63 F1
   Z-Wave Debug                    . .  dimmerSetLevel: node 064, endpoint None, value 99
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" status update brightness 100
   Z-Wave Debug                    queueing energy request of "064 - Dimmer Switch (LZW31-SN)" (activity detected)
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 40 05 5B 03 CA 80 02 A5
   Z-Wave Debug                    . .  sceneActivateCmd2: node 064, type: 0, scene: 2
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" up button pressed
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" status update is off
   Z-Wave Debug                    ignoring duplicate energy request of "064 - Dimmer Switch (LZW31-SN)" (activity detected)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 10 00 04 00 40 0A 32 02 21 34 00 00 00 75 00 00 F1
   Z-Wave Debug                    . .  requestMeterLevel: node 064, endpoint None, meterType 01, raw value 3400...
   Z-Wave Debug                    . .  requestMeterLevel: 11.7 W (float: 11.700000)
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" power load to 11.7 W
   Z-Wave Debug                    RCVD dimmerSetLevel: 01 09 00 04 00 40 03 20 03 00 92
   Z-Wave Debug                    . .  dimmerSetLevel: node 064, endpoint None, value 0
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 40 05 5B 03 CB 80 01 A7
   Z-Wave Debug                    . .  sceneActivateCmd2: node 064, type: 0, scene: 1
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" down button pressed
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" status update is on
   Z-Wave Debug                    RCVD requestMeterLevel: 01 18 00 04 00 30 12 32 02 21 64 00 01 FD BB 00 3C 00 01 FD BB 00 00 00 00 88
   Z-Wave Debug                    . .  requestMeterLevel: node 048, endpoint None, meterType 01, raw value 6400...
   Z-Wave Debug                    . .  requestMeterLevel: 130.491 kWh (float: 130.491000)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 18 00 04 00 30 12 32 02 21 74 00 00 08 0A 00 00 00 00 00 00 00 00 00 00 A6
   Z-Wave Debug                    . .  requestMeterLevel: node 048, endpoint None, meterType 01, raw value 7400...
   Z-Wave Debug                    . .  requestMeterLevel: 2.058 W (float: 2.058000)
   Z-Wave                          received "Washer (Switch)" power load to 2.058 W
   Z-Wave Debug                    RCVD requestMeterLevel: 01 10 00 04 00 40 0A 32 02 21 34 00 00 00 00 00 00 84
   Z-Wave Debug                    . .  requestMeterLevel: 0.0 W (float: 0.000000)
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" power load to 0.0 W
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 40 05 5B 03 CC 80 02 A3
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 40 05 5B 03 CD 80 01 A1
   Z-Wave Debug                    polling status of node "064 - Dimmer Switch (LZW31-SN)" (post-activity energy request)
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 40 03 32 01 00 25 AD 1E
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 AD 00 00 0C 4A (node ACK)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 40 0E 32 02 21 64 00 00 02 8B 66 D1 00 00 02 76 9E
   Z-Wave Debug                    . .  requestMeterLevel: node 064, endpoint None, meterType 01, raw value 6400...
   Z-Wave Debug                    . .  requestMeterLevel: 0.651 kWh (float: 0.651000)
   Z-Wave                          received "064 - Dimmer Switch (LZW31-SN)" energy total to 0.651 kWh
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 40 03 32 01 10 25 AE 0D
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 AE 00 00 0C 49 (node ACK)
   Z-Wave Debug                    RCVD sensorSetLevel: 01 09 00 04 00 36 03 20 01 00 E6
   Z-Wave Debug                    . .  sensorSetLevel: node 054, endpoint None, cmdClass 20, value 0
   Z-Wave                          received "M's Room (Motion)" status update is off
   Z-Wave Debug                    RCVD requestAlarmSensorStatus: 01 10 00 04 00 36 0A 71 05 00 00 00 FF 07 00 00 00 5B
   Z-Wave Debug                    . .  requestAlarmSensorStatus: node 054, endpoint None, cmdClass 71, type 0, value 0, classSubKey 710000
   Z-Wave Debug                    . .  requestAlarmSensorStatus: typeExt 7, valueExt 0, classSubKeyExt 7100000700
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 3D 0E 32 02 21 44 00 00 00 00 01 2D 00 00 00 00 A5
   Z-Wave Debug                    . .  requestMeterLevel: node 061, endpoint None, meterType 01, raw value 4400...
   Z-Wave Debug                    . .  requestMeterLevel: 0.00 kWh (float: 0.000000)
   Z-Wave Debug                    SENT requestDimmerStatus: 01 09 00 13 40 02 26 02 25 AF 09
   Z-Wave Debug                    RCVD requestDimmerStatus: 01 07 00 13 AF 00 00 06 42 (node ACK)
   Z-Wave                          sent "064 - Dimmer Switch (LZW31-SN)" status request
   Z-Wave                          sent "064 - Dimmer Switch (LZW31-SN)" energy status request
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 3D 0E 32 02 21 54 00 00 00 00 01 2D 00 00 00 00 B5
   Z-Wave Debug                    . .  requestMeterLevel: node 061, endpoint None, meterType 01, raw value 5400...
   Z-Wave Debug                    . .  requestMeterLevel: 0.00 W (float: 0.000000)
   Z-Wave Debug                    RCVD sensorSetLevel: 01 09 00 04 00 36 03 20 01 FF 19
   Z-Wave Debug                    . .  sensorSetLevel: node 054, endpoint None, cmdClass 20, value 255
   Z-Wave                          received "M's Room (Motion)" status update is on
   Z-Wave Debug                    RCVD requestDimmerStatus: 01 09 00 04 00 40 03 26 03 00 94
   Z-Wave Debug                    . .  requestDimmerStatus: node 064, endpoint None, value 0
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 40 03 32 01 00 25 B0 03
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 B0 00 00 10 4B (node ACK)
   Z-Wave Debug                    RCVD requestAlarmSensorStatus: 01 10 00 04 00 36 0A 71 05 00 00 00 FF 07 08 00 00 53
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 40 0E 32 02 21 64 00 00 02 8B 00 04 00 00 02 8B D0
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 40 03 32 01 10 25 B1 12
Fri Jul 03, 2020 5:31 pm
brettlid offline
Discovered all my Inovelli LZW31-SN switches report the wrong state after pressing the down button, when the light is off. The light will stay off but Indigo changes the state to on. If I hit the status request Indigo updates to the correct state. The same behavior happens if you hit the up paddle when the light is already on. Indigo changes the state to off, even though the light is on. A status request updates the correct state.
Thanks, Brett
Sat Jul 04, 2020 2:02 pm
Can you turn on Indigo's Z-Wave debug logging and capture what is being sent in both of those cases?
Mon Jul 06, 2020 7:44 am
brettlid offline
light was on, pressed the down button to turn it off. Pressed the down button again while it was off. (status shows on - lite is off)
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 15 05 5B 03 06 80 01 3F
   Z-Wave Debug                    . .  sceneActivateCmd2: node 021, type: 0, scene: 1
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" down button pressed
   Z-Wave Debug                    RCVD dimmerSetLevel: 01 09 00 04 00 15 03 20 03 00 C7
   Z-Wave Debug                    . .  dimmerSetLevel: node 021, endpoint None, value 0
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" status update is off
   Z-Wave Debug                    queueing energy request of "021 - Dimmer Switch (LZW31-SN)" (activity detected)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 10 00 04 00 15 0A 32 02 21 34 00 00 00 00 00 00 D1
   Z-Wave Debug                    . .  requestMeterLevel: node 021, endpoint None, meterType 01, raw value 3400...
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" power load to 0.0 W
   Z-Wave Debug                    polling status of node "021 - Dimmer Switch (LZW31-SN)" (post-activity energy request)
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 00 25 13 F5
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 13 00 00 02 FA (node ACK)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 15 0E 32 02 21 64 00 00 00 0B 00 0D 00 00 00 0B 8C
   Z-Wave Debug                    . .  requestMeterLevel: node 021, endpoint None, meterType 01, raw value 6400...
   Z-Wave Debug                    . .  requestMeterLevel: 0.011 kWh (float: 0.011000)
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 10 25 14 E2
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 14 00 00 03 FC (node ACK)
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 15 05 5B 03 07 80 01 3E
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" status update is on
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 00 25 15 F3
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 15 00 00 02 FC (node ACK)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 15 0E 32 02 21 64 00 00 00 0B 00 0B 00 00 00 0B 8A
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 10 25 16 E0
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 16 00 00 02 FF (node ACK)
/code]
pressed the up button while the light was off. Then pressed the up button again (status shows off - lite is on)
[code]
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 15 05 5B 03 08 80 02 32
   Z-Wave Debug                    . .  sceneActivateCmd2: node 021, type: 0, scene: 2
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" up button pressed
   Z-Wave Debug                    RCVD dimmerSetLevel: 01 09 00 04 00 15 03 20 03 46 81
   Z-Wave Debug                    . .  dimmerSetLevel: node 021, endpoint None, value 70
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" status update brightness 71
   Z-Wave Debug                    ignoring duplicate energy request of "021 - Dimmer Switch (LZW31-SN)" (activity detected)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 10 00 04 00 15 0A 32 02 21 34 00 00 00 37 00 00 E6
   Z-Wave Debug                    . .  requestMeterLevel: 5.5 W (float: 5.500000)
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" power load to 5.5 W
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 00 25 19 FF
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 19 00 00 02 F0 (node ACK)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 15 0E 32 02 21 64 00 00 00 0B 00 7E 00 00 00 0B FF
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 10 25 1A EC
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 1A 00 00 02 F3 (node ACK)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 10 00 04 00 15 0A 32 02 21 34 00 00 00 3E 00 00 EF
   Z-Wave Debug                    . .  requestMeterLevel: 6.2 W (float: 6.200000)
   Z-Wave                          received "021 - Dimmer Switch (LZW31-SN)" power load to 6.2 W
   Z-Wave Debug                    RCVD sceneActivateCmd2: 01 0B 00 04 00 15 05 5B 03 09 80 02 33
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 00 25 1B FD
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 1B 00 00 02 F2 (node ACK)
   Z-Wave Debug                    RCVD requestMeterLevel: 01 14 00 04 00 15 0E 32 02 21 64 00 00 00 0B 00 08 00 00 00 0B 89
   Z-Wave Debug                    SENT requestMeterLevel: 01 0A 00 13 15 03 32 01 10 25 1C EA
   Z-Wave Debug                    RCVD requestMeterLevel: 01 07 00 13 1C 00 00 03 F4 (node ACK)
Tue Jul 07, 2020 5:12 pm
Thanks for the details. I found the problem and it will be fixed in the next release of Indigo.
Wed Jul 08, 2020 9:15 am
brettlid offline
Fri Jul 10, 2020 10:19 pm
edrabbit offline
awesome, thanks!
