Sun Oct 20, 2019 12:26 pm
Ksullivan offline
I’m using Stella Z and the thermostat are Created using the smart devices plugin
Sun Oct 20, 2019 12:27 pm
Ksullivan offline
When I try to change the set point in indigo touch control page
Sun Oct 20, 2019 1:35 pm
autolog offline
Are you changing the setpoint on the TRV Controller controlling the Stella-Z, the Stella-Z itself or the Remote Stat? :?
Sun Oct 20, 2019 1:36 pm
Ksullivan offline
Remote stat
Sun Oct 20, 2019 2:02 pm
autolog offline
Ksullivan wrote:
Remote stat
OK, thanks - I haven't got an instant answer; I will try and find time to investigate the issue tomorrow. :)
Sun Oct 20, 2019 2:04 pm
Ksullivan offline
Thank you
Mon Oct 21, 2019 1:30 am
autolog offline
Hi Keith,
I need to see a device definition print for the remote stat.
Can you execute the following command from the Indigo Scripting Shell (see bottom of the Indigo plugin menu):
indigo.server.log(u"Remote Stat Device:\n {}".format(indigo.devices[12345678])
where 12345678 is the Indigo device Id of your remote stat device i.e. not the TRV Thermostat Controller. The output is written to the Indigo log if you could copy and paste it in a reply. :)
Mon Oct 21, 2019 4:19 am
shapa offline
Better now! :)
1) Without remote stat device specified - thermostat settings (including from UI and schedules) works but seeing
" TRV Error TRV Controller can't control TRV 'new device 2' as the TRV doesn't report temperature and there is no Remote Stat defined!"
2) When specifying remote stat device - it works OK (temperature is shown correctly), but theTF021 setpoint is always 5C - even in case I'm changing it, immediately reset by the TRV
I.e. no schedules or manual settings works
Some small error in the logic somewhere :)
Mon Oct 21, 2019 4:45 am
autolog offline
shapa wrote:
... 2) When specifying remote stat device - it works OK (temperature is shown correctly), but theTF021 setpoint is always 5C - even in case I'm changing it, immediately reset by the TRV ...
What setpoint are you changing: I need to know whether you are adjusting the physical device or an Indigo device and which one? :)
Mon Oct 21, 2019 6:00 am
shapa offline
Actually, tried everything, including TRV device delete and create.
1) Physical device (physical buttons) - resetting back to 5C in a few seconds ( Z-Wave sent "Conservatory HeatIT Thermostat" change heat setpoint to 5.0°)
2) Physical device via Indigo UI - resetting back to 5C in a few seconds ( Z-Wave sent "Conservatory HeatIT Thermostat" change heat setpoint to 5.0°)
3) TRV device - adjusting the temperature but physical device is not syncing / staying at 5C
Only happens when the "remote stat" is specified.
Screenshot 2019-10-21 12.58.04.png (432.86 KiB) Viewed 2768 times
Screenshot 2019-10-21 12.57.46.png (328.21 KiB) Viewed 2768 times
Mon Oct 21, 2019 7:21 am
autolog offline
Have you got Remote Setpoint Heat Adjustment enabled in the TRV Controller device settings?
What are you setting the setpoint to?
Mon Oct 21, 2019 11:16 am
shapa offline
No adjustment enabled
Any setpoint - tried 19, 20, 25, etc... Identical outcome - resetting back to 5C
Screenshot 2019-10-21 at 18.16.12.png (163.79 KiB) Viewed 2743 times
Mon Oct 21, 2019 12:05 pm
autolog offline
In the previous image your Air sensor (which is the remote stat?) is showing 26 deg C which I think is why it is setting the temp to 5 deg C i.e. effectively off.
It is more than 21 deg C. Is the 26 deg C correct?
Mon Oct 21, 2019 1:13 pm
Ksullivan offline
Hi John
The shell command doesnt seem to work as im getting a timed out :( Any ideas?
indigo.server.log(u"Remote Stat Device:\n {}".format(indigo.devices[1834533522])
2019-10-21 20:10:07.174 IndigoPluginHost[86035:1838786] ConnectionRequest() caught exception: ServerCommunicationError -- timeout waiting for server to start
2019-10-21 20:10:07.175 IndigoPluginHost[86035:1838767]
connection to server failed or was dropped
Mon Oct 21, 2019 1:20 pm
shapa offline
Tried to set 32C - the same issue, resetting to 5C :)
Is it possible to add a setting to be able to switch on / off the setpoint logic? For a smart floor thermostat - only schedules (with setpoints) are required. TF021 will automatically do the rest. However, the logic could be very useful in case of a "dumb" relay controlling underfloor heating - so it would be nice to make it configurable.
Screenshot 2019-10-21 20.17.04.png (404.63 KiB) Viewed 2716 times
Page 18 of 28 1 ... 15, 16, 17, 18, 19, 20, 21 ... 28
