Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Fri May 22, 2020 10:41 am
by cesarvog
Hello everyone,

I've installed two units of this dual relay switch, so we could automate control of 4 different loads (Load 1 / Load 2 in each ZWN-RSM2-PLUS). even though I would like to automate the loads, I also would like to maually control the same loads by using regular switches locally. This unit allows it if you install old school switches locally and connect those to the AUX 1/ AUX 2 terminals of the ZWN-RSM2-PLUS.

Once I paired the units with Indigo, I was immediately able to control the 4 loads, either operating the manual switches locally (i.e. pressing each of the 2 buttons installed locally on either ZWN-RSM2-PLUS), or centrally (i.e using Indigo to send on/off commands to control each load).

The problem I'm facing is: Instant Status reports only seem to report local changes (button presses) for Load1 on both ZWN-RSM2-PLUS units... I have tried to resync, but wasn't able to overcome this issue.

Below is the log contents captured immediately after resyncing and pressing buttons for load 1 and load 2 on one of my ZWN-RSM2-PLUS units. As you can see at the end of the log, only load 1 seem to be reported back to Indigo. The same thing happens oh my other ZWN-RSM2-PLUS unit, so it doesn't seem to be cause by a malfunctioning unit

22 May 2020 12:58:07
Z-Wave Syncing - started for "Hall - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 1"
Z-Wave Syncing - retrieved module neighbors list: 1, 20, 44, 47, 49, 51, 55, 57, 60, 63, 68, 69, 70, 72, 75, 80, 92, 101, 112, 114
Z-Wave Syncing - assigning return route to "113 - Hall - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 1"
Z-Wave Syncing - assigned return route
Z-Wave Syncing - retrieved manufacture and model names: Enerwave - 011A, Relay Power Switch - 01110606
Z-Wave Syncing - retrieved protocol version 4.38, app version 5.12
Z-Wave Syncing - retrieved class hierarchy: Routing Slave : Relay Switch : Relay Power Switch (04 : 10 : 01, base 25)
Z-Wave Syncing - retrieved command classes: 20v1 60v4 25v1 86v1 27v1 8Ev1 72v1 73v1 59v1 5Av1 5Ev1 85v1
Z-Wave Syncing - retrieved encrypt commands: - none -
Z-Wave Syncing - retrieved capabilities: routing, beaming
Z-Wave Syncing - retrieved multi-endpoint types: 1:(10 : 01), 2:(10 : 01)
Z-Wave Syncing - retrieved multi-endpoint classes: 1:[25 20], 2:[25 20]
Z-Wave Syncing - retrieved group 1 associations: [1]
Z-Wave Syncing - retrieved group 2 associations: []
Z-Wave Syncing - retrieved group 3 associations: []
Z-Wave Syncing - group 1 association to interface already exists (skipping)
Z-Wave Syncing - complete
Z-Wave sent "Hall - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 1" status request
Z-Wave sent "Hall - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 2" status request
Z-Wave received "Sensor Varanda - Dry Contact" status update is on
Z-Wave received "Sensor Varanda - Dry Contact" status update is off

22 May 2020 12:58:57
Z-Wave received "Hall - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 1" status update is on

Can anyone please advise how to make Load 2 also report back to Indigo via Instant Status reports?

TIA
Cesar

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Fri May 22, 2020 12:29 pm
by matt (support)
Hi Cesar,

Turn on Indigo's Z-Wave Debug logging checkbox (via the Interfaces->Z-Wave->Configure... menu), then manually control both loads and copy/paste the Event Log results of each individually into a follow-up post.

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Fri May 22, 2020 12:32 pm
by matt (support)
Actually, based on the manual it looks like by default that functionality is disabled. Try using Indigo's Interfaces->Z-Wave->Modify Configuration Parameter... menu to change parameter #3 to the value of 1. If that doesn't work then turn on the debug logging as mentioned above to try to capture what (if anything) the module is sending.

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Sat May 23, 2020 1:09 pm
by cesarvog
Thanks Matt for prompt reply,
When I tried "Interfaces->Z-Wave->Modify Configuration Parameter...", none of my Enerwave ZWN-RSM2-PLUS units appeared on the list of available devices to send parameter to...
I have seen additional posts mentioning that for a device to accept parameters modifications, it has to support Modification Class. As you can see from the sync log above, mine do not seem to support it... I've also seen one of your posts suggesting to remove and add again with encryption, but did not have the time to do that yet, as both units are now inside the walls...
Any other ideas?

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Sat May 23, 2020 1:17 pm
by cesarvog
Here is the log, after setting z-wave debug logins on. As requested, I manually switched both local buttons ON, waited 1 second, then switched both OFF. Log only captured ON and OFF for Relay Switch 1, which corresponds to one of the local buttons.

Z-Wave Debug RCVD getNodeProtocolInfo: 01 09 01 41 D3 9C 01 04 10 01 ED (no inbound callback)
Z-Wave Debug . . getNodeProtocolInfo: node 112, class name: Relay Power Switch
Z-Wave Debug . . getNodeProtocolInfo: class hierarchy: Routing Slave : Relay Switch : Relay Power Switch (04 : 10 : 01)
Z-Wave Debug . . getNodeProtocolInfo: base class command: 25
Z-Wave Debug . . getNodeProtocolInfo: supported class commands: 20 25 27
Z-Wave Debug . . getNodeProtocolInfo: encrypt class commands:
Z-Wave Debug . . getNodeProtocolInfo: features: routing, beaming
Z-Wave Debug SENT getNodeProtocolInfo: 01 04 00 41 71 CB
Z-Wave Debug RCVD getNodeProtocolInfo: 01 09 01 41 D3 9C 01 04 10 01 ED (no inbound callback)
Z-Wave Debug . . getNodeProtocolInfo: node 113, class name: Relay Power Switch
Z-Wave Debug . . getNodeProtocolInfo: class hierarchy: Routing Slave : Relay Switch : Relay Power Switch (04 : 10 : 01)
Z-Wave Debug . . getNodeProtocolInfo: base class command: 25
Z-Wave Debug . . getNodeProtocolInfo: supported class commands: 20 25 27
Z-Wave Debug . . getNodeProtocolInfo: encrypt class commands:
Z-Wave Debug . . getNodeProtocolInfo: features: routing, beaming
Z-Wave Debug SENT getNodeProtocolInfo: 01 04 00 41 72 C8
Z-Wave Debug RCVD getNodeProtocolInfo: 01 09 01 41 D3 9C 01 04 10 01 ED (no inbound callback)
Z-Wave Debug . . getNodeProtocolInfo: node 114, class name: Relay Power Switch
Z-Wave Debug . . getNodeProtocolInfo: class hierarchy: Routing Slave : Relay Switch : Relay Power Switch (04 : 10 : 01)
Z-Wave Debug . . getNodeProtocolInfo: base class command: 25
Z-Wave Debug . . getNodeProtocolInfo: supported class commands: 20 25 27
Z-Wave Debug . . getNodeProtocolInfo: encrypt class commands:
Z-Wave Debug . . getNodeProtocolInfo: features: routing, beaming
Z-Wave Debug starting node healing thread
Z-Wave Debug starting node status polling thread
Z-Wave Debug RCVD requestRelayStatus: 01 09 00 04 00 71 03 25 03 FF 59
Z-Wave Debug . . requestRelayStatus: node 113, endpoint None, value 255
Z-Wave received "Hall - Int. Santa - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 1" status update is on
Z-Wave Debug RCVD requestRelayStatus: 01 09 00 04 00 71 03 25 03 00 A6
Z-Wave Debug . . requestRelayStatus: node 113, endpoint None, value 0
Z-Wave received "Hall - Int. Santa - Enerwave ZWN-RSM2-PLUS Dual Relay Switch 1" status update is off
Z-Wave Debug RCVD requestMeterLevel: 01 14 00 04 00 41 0E 32 02 21 64 00 00 07 12 02 58 00 00 07 12 8F
Z-Wave Debug . . requestMeterLevel: node 065, endpoint None, meterType 01, raw value 6400...
Z-Wave Debug . . requestMeterLevel: 1.810 kWh (float: 1.810000)
Z-Wave Debug RCVD requestMeterLevel: 01 10 00 04 00 41 0A 32 02 21 74 00 00 00 00 00 00 C5
Z-Wave Debug . . requestMeterLevel: node 065, endpoint None, meterType 01, raw value 7400...
Z-Wave Debug . . requestMeterLevel: 0.000 W (float: 0.000000)

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Tue Jun 02, 2020 2:32 pm
by cesarvog
Checking in, to see if anyone knows how to fix this issue.

TIA
Cesar

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Tue Jun 02, 2020 3:21 pm
by matt (support)
Unfortunately, I don't know why the module isn't sending updates for the 2nd switch. As shown in your Event Log nothing is sent except when you controlled the first switch. You are correct about Indigo not showing that device in the Modify Configuration Parameter UI because the device doesn't report (during the sync) to support that command class (0x70). You can try excluding and re-including it with encryption, but I"m not sure that is going to help. I don't know if you are running into a limitation of how the module works, or if the particular model you have is an older (and buggy) firmware version. From the log though this doesn't appear to be a device definition issue, as there are no commands coming from the module at all when the 2nd button is pressed. If there were commands being sent but just to a different endpoint than Indigo expected, then a device definition could fix the problem.

Re: Enerwave ZWN-RSM2-PLUS Dual Relay Switch

PostPosted: Wed Jun 03, 2020 7:07 am
by cesarvog
Thanks, Matt.

I will look into trying exclude / re-include with encryption, to see if solves the issue. I don't think it will do any good, but we won't know until I try... It won't happen for a few days as I'm busy with other house renovation issues.

Best regards,
Cesar