American Standard 624 Thermostat Humidity Reporting Issue
Posted: Sun Nov 17, 2019 3:56 pm
I have an American Standard 624 Thermostat (TCONT624) which is the same as the Trane XL624, and love it. Works great with Indigo. The only issue I've found is a minor one. When Indigo polls the device for status or when I press the button to send a status request. the humidity value is not returned. All other values are returned as expected. Here's a snippet of the log file:
Any thoughts as to why the humidity values is not being returned correctly?
Thanks,
-Tommy
- Raw command sent (Node 25): 01 09 00 13 19 02 45 02 25 D9 45 (True)
sent "Thermostat" fan state status request
received "Thermostat" fan is on
Raw command received (Node 25): 01 09 00 04 00 19 03 45 03 01 AF
Raw command sent (Node 25): 01 0A 00 13 19 03 31 04 05 25 DA 33 (True)
sent "Thermostat" humidity status request
Raw command sent (Node 25): 01 09 00 13 19 02 31 04 25 DB 35 (True)
sent "Thermostat" temperature status request
received "Thermostat" temperature update to 67 °F
Raw command received (Node 25): 01 0B 00 04 00 19 05 31 05 01 09 43 93
Raw command sent (Node 25): 01 0A 00 13 19 03 43 02 01 25 DC 45 (True)
sent "Thermostat" heat setpoint status request
received "Thermostat" heat setpoint is 70 °F
Raw command received (Node 25): 01 0B 00 04 00 19 05 43 03 01 09 46 E2
- sent "Thermostat" raw command [31 04 05 25]
Raw command sent (Node 25): 01 0B 00 13 19 04 31 04 05 25 25 DE 14 (True)
received "Thermostat" humidity update to 44%
Raw command received (Node 25): 01 0B 00 04 00 19 05 31 05 05 01 2C F0
- 0x31 0x04 0x05 0x25
0x31-COMMAND_CLASS_SENSOR_MULTILEVEL
0x04-SENSOR_MULTILEVEL_GET
0x05-Sensor Type of Humidity
0x25-Scale (0010 0101)
- Reserved 001
Scale 00: Percentage value (%)
Reserved 101
Any thoughts as to why the humidity values is not being returned correctly?
Thanks,
-Tommy