Black Cat (by Philio) Dual In-Wall Relay Status Issue

Posted on
Mon Oct 15, 2018 7:29 am
matt (support) offline
Site Admin
User avatar
Posts: 21417
Joined: Jan 27, 2003
Location: Texas

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

I'm a bit confused. On your spreadsheet you have columns for R1, R2, and R2. Which one of those is the first device shown in the tabbed devices dialog ("Both Relays")? Do you really mean:

R1 is R1+R2
R2 is R1 Only
R3 is R2 Only

Image

Posted on
Mon Oct 15, 2018 3:16 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Apologies for my “short hand”.
R1 and R2 are the two physical switches as marked on the device and shown in the Indigo UI.
R3 is the “Both Relays” device shown in the Indigo UI

Definitely not so simples, eh??!!


Sent from my iPhone using Tapatalk

Posted on
Thu Oct 18, 2018 11:52 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Was any of that data meaningful? Or should I abandon these devices?


Sent from my iPhone using Tapatalk

Posted on
Fri Oct 19, 2018 11:39 am
matt (support) offline
Site Admin
User avatar
Posts: 21417
Joined: Jan 27, 2003
Location: Texas

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Just haven't had time to investigate it in detail yet.

Image

Posted on
Sun May 12, 2019 4:36 pm
matt (support) offline
Site Admin
User avatar
Posts: 21417
Joined: Jan 27, 2003
Location: Texas

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Indigo 7.3 (and 7.3.1) are now available and should improve the problems reported above for the Black Cat Double Relay Module (ZWBCL2).

Image

Posted on
Mon May 13, 2019 5:39 am
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Thanks, Matt.

Working just fine on the bench.

Thanks again,

mclass


Sent from my iPad using Tapatalk

Posted on
Sun Feb 16, 2020 10:28 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

After a long time since I last used one of these devices, I dug one out for an application where I want to use the S1 and S2 inputs to control and/or monitor. It appears that these inputs will operate the relay, but will not report back to Indigo, unless I poll them. Is there anything obvious (like a parameter change) that might rectify this issue? This is what Indigo reports about the device:
Z-Wave Indigo Device "086 - Both Relays" Z-Wave Properties:
Indigo Z-Wave Version: 7.4.1
Node ID: 86
Model: Double Relay Module (ZWBCL2)
Model ID: 00010013
Manufacturer: Philio
Manufacturer ID: 013C
Protocol Version: 3.95
Application Version: 1.08
Model Definition Version: 4
Library Type: 3
Class Name: Relay Power Switch
Class Hierarchy: 04 : 10 : 01
Command Class Base: 25
Command Versions: 20v1 85v1 86v1 59v1 5Av1 5Ev1 60v3 25v1 27v1 2Bv1 2Cv1 70v1 71v1 72v1 73v1 75v1 7Av1
Encryption Status: Not Supported
Multi-Endpoint Types: 1:(10 : 01), 2:(10 : 01), 3:(10 : 01)
Multi-Endpoint Classes: 1:[25 20], 2:[25 20], 3:[25 20]
Multi-Instance Counts: - none -
Features: routing, beaming
Neighbors: 1, 9, 11, 12, 13, 18, 19, 24, 29, 44, 59, 70
Associations: 1:[1] 2:[1] 3:[1]
Config Values: - none -


A copy of the manual can be found here:
https://www.dropbox.com/s/jtryao5i23ykl ... 5.pdf?dl=0

TIA

mclass

Posted on
Wed Mar 04, 2020 7:09 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

On returning to this device with a little more time than usual (!), I have discovered that the S1 and S2 inputs will operate the individual relays, but the relay reports back "globally" that the overall device is on ie operation of either relay will report that the device is on.

My workaround in this instance is a trigger that on receipt of the global "relay on" report will update the status of each of the individual relays. Not ideal, but I guess it allows use of these devices as required!

Posted on
Fri Mar 06, 2020 1:07 am
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Turn on Zwave debug or put a Zwave Watcher on it, then operate both inputs on/off a few times, and post log here.


Sent from my iPhone using Tapatalk Pro

Posted on
Sun Mar 08, 2020 7:47 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Thanks for your offer, and apologies for delayed reply - it's been a holiday weekend here!!

The Black Cat relay presents as three devices "Black Cat" (home or principal device), "Relay 1" and "Relay 2". The manual can be found here:
https://www.dropbox.com/s/jtryao5i23ykl ... 5.pdf?dl=0

Here's the ZWave Watcher logs for operation of the device:

Operate Black Cat relay ("home" device) from Indigo:
Code: Select all
  Z-Wave                          sent "010 -Black Cat" on
   Z-Wave Watcher Debug            Raw command sent (Node 10): 01 0A 00 13 0A 03 25 01 FF 25 33 22 (True)
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 FF 22
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 FF 22
   Z-Wave                          sent "010 -Black Cat" off
   Z-Wave Watcher Debug            Raw command sent (Node 10): 01 0A 00 13 0A 03 25 01 00 25 34 DA (True)
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 00 DD
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 00 DD


Relay 1 operation from Indigo:
Code: Select all
 Z-Wave                          sent "010 - Relay 1" on
   Z-Wave Watcher Debug            Raw command sent (Node 10 Endpoint 1): 01 0E 00 13 0A 07 60 0D 01 01 25 01 FF 25 35 49 (True)
   Z-Wave                          received "010 -Black Cat" status update is on
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 FF 22
   Z-Wave                          sent "010 - Relay 1" off
   Z-Wave Watcher Debug            Raw command sent (Node 10 Endpoint 1): 01 0E 00 13 0A 07 60 0D 01 01 25 01 00 25 36 B5 (True)
   Z-Wave                          received "010 -Black Cat" status update is off
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 00 DD


Relay 2 operation from Indigo:
Code: Select all
  Z-Wave                          sent "010 - Relay 2" on
   Z-Wave Watcher Debug            Raw command sent (Node 10 Endpoint 2): 01 0E 00 13 0A 07 60 0D 01 02 25 01 FF 25 37 48 (True)
   Z-Wave                          received "010 -Black Cat" status update is on
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 FF 22
   Z-Wave                          sent "010 - Relay 2" off
   Z-Wave Watcher Debug            Raw command sent (Node 10 Endpoint 2): 01 0E 00 13 0A 07 60 0D 01 02 25 01 00 25 38 B8 (True)
   Z-Wave                          received "010 -Black Cat" status update is off
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 00 DD


Relay 1 ON/OFF operation using S1 input:
Code: Select all
Z-Wave                          received "010 -Black Cat" status update is on
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 FF 22
   Z-Wave                          received "010 -Black Cat" status update is off
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 00 DD


Relay 2 ON/OFF operation using S2 input:
Code: Select all
 Z-Wave                          received "010 -Black Cat" status update is on
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 FF 22
   Z-Wave                          received "010 -Black Cat" status update is off
   Z-Wave Watcher Debug            Raw command received (Node 10): 01 09 00 04 00 0A 03 25 03 00 DD


Any suggestions gratefully received!!
TIA

mclass

Posted on
Tue Mar 10, 2020 2:56 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Hi.

Can you check what associations are set on the device?

Indigo > Interfaces > Zwave > Manage associations

Select node 10 then see what nodes are associated to groups 1, 2 and 3.

I suspect you only have Indigo (node 1) associated to group 1, and nothing associated to groups 2 and 3.

You'll need to associate Indigo (node 1) to groups 2 and 3, then repeat the above tests.

Your device is sending "On" if any relay is on, or "Off" if both are off, to group 1 (Indigo).
It additionally sends "Relay 1 is On/Off" to group 2 (currently nobody) and "Relay 2 is On/Off" to group 3 (currently nobody).

Once you add associations for groups 2 and 3, Indigo will then receive those separate relay on/off status updates - and we can then see if Matt/Jay have programmed it to intercept them or whether they have further work to do.

Peter

Posted on
Wed Mar 11, 2020 11:18 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Hi Peter!

Thanks for your advice, and apologies for the slow reply - I've been away from the house and haven't been able to check until now.

Indigo has been associated with all three groups. But just to check, I re-associated each group and then performed a re-synch. This is what was logged:

Code: Select all
Syncing - started for "010 -Black Cat"
   Z-Wave                          Syncing - retrieved module neighbors list: 1, 7, 9
   Z-Wave                          Syncing - assigning return route to "010 - 010 -Black Cat"
   Z-Wave                          Syncing - assigned return route
   Z-Wave                          Syncing - retrieved manufacture and model names: Philio - 013C, Double Relay Module (ZWBCL2) - 00010013
   Z-Wave                          Syncing - retrieved protocol version 3.95, app version 1.08
   Z-Wave                          Syncing - retrieved class hierarchy: Routing Slave : Relay Switch : Relay Power Switch (04 : 10 : 01, base 25)
   Z-Wave                          Syncing - retrieved command classes: 20v1 60v3 25v1 86v1 27v1 2Bv1 2Cv1 70v1 71v1 72v1 73v1 75v1 59v1 5Av1 7Av1 5Ev1 85v1
   Z-Wave                          Syncing - retrieved encrypt commands: - none -
   Z-Wave                          Syncing - retrieved capabilities: routing, beaming
   Z-Wave                          Syncing - retrieved multi-endpoint types: 1:(10 : 01), 2:(10 : 01), 3:(10 : 01)
   Z-Wave                          Syncing - retrieved multi-endpoint classes: 1:[25 20], 2:[25 20], 3:[25 20]
   Z-Wave                          Syncing - retrieved group 1 associations: [1]
   Z-Wave                          Syncing - retrieved group 2 associations: [1]
   Z-Wave                          Syncing - retrieved group 3 associations: [1]
   Z-Wave                          Syncing - group 1 association to interface already exists (skipping)
   Z-Wave                          Syncing - group 2 association to interface already exists (skipping)
   Z-Wave                          Syncing - group 3 association to interface already exists (skipping)
   Z-Wave                          Syncing - complete
   Z-Wave                          sent "010 -Black Cat" status request
   Z-Wave                          sent "010 - Relay 1" status request
   Z-Wave                          sent "010 - Relay 2" status request


Note that a status request (sent manually) will retrieve the correct status of R1 and R2.

Any further help appreciated - otherwise I'll opt for another brand of dual relay!! :shock:

Thanks again,

Mclas

Posted on
Thu Mar 12, 2020 1:04 am
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Out of interest can you check the value of parameters 1 and 6?

And what us polling set to?


Sent from my iPhone using Tapatalk Pro

Posted on
Thu Mar 12, 2020 6:09 pm
mclass offline
Posts: 315
Joined: May 13, 2015
Location: Melbourne, Australia

Re: Black Cat (by Philio) Dual In-Wall Relay Status Issue

Out of interest can you check the value of parameters 1 and 6?

All parameters are set to defaults, with:
Parameter 1 = 3 (Relays 1 & 2)
Parameter 6 = 1 (Endpoint 3 exists)

And what us polling set to?

Polling is set to "Only when activity is detected" . I had previously trialed "As often as possible". That worked but was slow in detecting changes, and sloooowed the whole system down!

mclass