@Martyn:
You must NOT do a FULL reset after you have enabled input 2 notifications (param 100 to 9).
You do ONLY a SOFT reset which means that you keep the service button pushed more than 2 seconds but less than 6 seconds when controller is in exclusion mode.
If I remember the procedure correctly here is how I did to get temp sensor working and updating in Indigo:
Start with doing a factory reset WITHOUT temp sensor connected to make sure that the device is "clean" from all config parameters and in default mode:
1. Do a full exclusion with factory reset of the parameters when the temp sensor is NOT connected. Do the exclusion to factory settings by these two methods:
if connected to 24VDC (my preferred method) then keep the service button pushed MORE than 6 seconds when controller is in exclusion mode
or
if connected to 240VAC then you must press I1 five times within 3 seconds during the first 60 seconds when powering on the device
2. Disconnect the device from power and wait at least 30 seconds
3. Connect temp sensor to device
4. Put controller in inclusion mode
5. Power on the device and it should auto-include within 30 seconds. Note that the auto-inclusion is only active 5 seconds after you power on the device so you must put the controller FIRST into inclusion mode and then you power on the device. If auto-inclusion does not work then you can either
if connected to 24VDC (my preferred method) then keep the service button pushed MORE than 2 seconds BUT LESS than 6 seconds when controller is in inclusion mode. This time window of 2 to 6 seconds is important since if you press the service button more than 6 seconds then you are doing a full factory reset again
or
if connected to 240VAC then you must press I1 three times within 3 seconds during the first 60 seconds when powering on the device
6. Now enable input 2 notifications in Indigo.
7. Time for the soft reset!
Set your controller/Indigo into exclusion mode
if connected to 24VDC (my preferred method) then keep the service button pushed MORE than 2 seconds BUT LESS than 6 seconds when controller is in inclusion mode. This time window of 2 to 6 seconds is important since if you press the service button more than 6 seconds then you are doing a full factory reset again
or
if connected to 240VAC then you must press I1 three times within 3 seconds during the first 60 seconds when powering on the device
8. After the soft exclude is finished disconnect device from power and wait at least 30 seconds.
9. Set your controller into inclusion mode and reconnect device to power.
It should autoinclude within 30 seconds but if it does not do the same process as I described in 5 above.
The Qubino Flush 1D relay with temp sensor should now work properly.
All above info found in the manual where you can download from for example
https://products.z-wavealliance.org/Pro ... _1.6.2.pdf Read page 38 and 39 and 45.
I have experienced a problem where the temp update suddenly stops reporting even though the on/off function works fine. Power cycling the device gets the temp updates back. I have not received back an answer from Qubino about this issue.
My Qubino Flush 1D relay has firmware 4.00 according to the device info in Indigo. What firmware do you have?