DSC Alarm Plugin (Locked)

Posted on
Mon Jun 27, 2011 3:57 pm
peppop offline
User avatar
Posts: 104
Joined: Oct 18, 2006
Location: Mas

Re: DSC Alarm Plugin

I'm using a IT-100. I also have a escort module and thermostat and a intercom module connected to the alarm. Could that be giving me the errors? Also, I'm not getting any info on LCDLine 1= and LCDLine2 =. Here is the log. Thank You.
Code: Select all
Jun 27, 2011 5:47:30 PM
  Enabling plugin "DSC Alarm 0.9.0"
  Starting plugin "DSC Alarm 0.9.0"
  Plugin "DSC Alarm" connected
  Plugin "DSC Alarm 0.9.0" started
  DSC Alarm Debug                 Entered createVariables
  DSC Alarm Debug                 Variable folder exists by ID
  DSC Alarm Debug                 SHOW: Data : (dict)
     code : 1364 (string)
     createVariables : true (bool)
     serialPort : /dev/cu.USA19H41P1.1 (string)
     showDebugInfo : true (bool)
     speakTextArmed : The alarm is now armed. (string)
     speakTextArming : The alarm will arm in 30 seconds. (string)
     speakTextDisarmed : The alarm is disarmed, welcome home. (string)
     speakTextEntryDelay : Please enter your access code. (string)
     speakTextFailedToArm : The alarm cannot be armed. (string)
     speakTextTripped : Warning, intruder alert. (string)
     speakingEnabled : true (bool)
     variableFolder : 1995410466 (integer)
     variableState : 1370202975 (integer)
  DSC Alarm Debug                 Serial port opened
  DSC Alarm Debug                 Pinging alarm panel.
  DSC Alarm Debug                 TX: 00090

  DSC Alarm Debug                 RX: 50000025

  DSC Alarm Debug                 ACK for cmd 000.
  DSC Alarm                       Communication Initialized.
  DSC Alarm Debug                 Requesting full state update.
  DSC Alarm Debug                 TX: 00191

  DSC Alarm Debug                 RX: 50000126

  DSC Alarm Debug                 ACK for cmd 001.
  DSC Alarm Debug                 RX: 908010011C4

  DSC Alarm Debug                 DSC Software Version 01.00
  DSC Alarm Debug                 RX: 6531CF

  DSC Alarm Debug                 Cmd:653 Dat:1 Sum:207
  DSC Alarm Debug                 RX: 6732D2

  DSC Alarm Debug                 Partition 2 Busy.
  DSC Alarm Debug                 RX: 6733D3

  DSC Alarm Debug                 Partition 3 Busy.
  DSC Alarm Debug                 RX: 6734D4

  DSC Alarm Debug                 Partition 4 Busy.
  DSC Alarm Debug                 RX: 6735D5

  DSC Alarm Debug                 Partition 5 Busy.
  DSC Alarm Debug                 RX: 6736D6

  DSC Alarm Debug                 Partition 6 Busy.
  DSC Alarm Debug                 RX: 6737D7

  DSC Alarm Debug                 Partition 7 Busy.
  DSC Alarm Debug                 RX: 6738D8

  DSC Alarm Debug                 Partition 8 Busy.
  DSC Alarm Debug                 RX: 8411CE

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 1)
  DSC Alarm Debug                 RX: 8412CF

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 2)
  DSC Alarm Debug                 RX: 8413D0

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 3)
  DSC Alarm Debug                 RX: 8414D1

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 4)
  DSC Alarm Debug                 RX: 8415D2

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 5)
  DSC Alarm Debug                 RX: 8416D3

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 6)
  DSC Alarm Debug                 RX: 8417D4

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 7)
  DSC Alarm Debug                 RX: 8418D5

  DSC Alarm Debug                 Trouble Status Restore (LED OFF). (Partition 8)
  DSC Alarm Debug                 RX: 90311FE

  DSC Alarm Debug                 LED 'Ready' is 'on'.
  DSC Alarm Debug                 RX: 90320FE

  DSC Alarm Debug                 LED 'Armed' is 'off'.
  DSC Alarm Debug                 RX: 90330FF

  DSC Alarm Debug                 LED 'Memory' is 'off'.
  DSC Alarm Debug                 RX: 9034000

  DSC Alarm Debug                 LED 'Bypass' is 'off'.
  DSC Alarm Debug                 RX: 9035001

  DSC Alarm Debug                 LED 'Trouble' is 'off'.
  DSC Alarm Debug                 RX: 9036002

  DSC Alarm Debug                 LED 'Program' is 'off'.
  DSC Alarm Debug                 RX: 9037003

  DSC Alarm Debug                 LED 'Fire' is 'off'.
  DSC Alarm Debug                 RX: 9038105

  DSC Alarm Debug                 LED 'Backlight' is 'on'.
  DSC Alarm Debug                 RX: 9039005

  DSC Alarm Debug                 LED 'AC' is 'off'.
  DSC Alarm Debug                 RX: 61000128

  DSC Alarm Debug                 Zone number 1 Closed.
  DSC Alarm                       Alarm Zone 'Front door' Closed.
  DSC Alarm Debug                 RX: 61000229

  DSC Alarm Debug                 Zone number 2 Closed.
  DSC Alarm Debug                 RX: 6100032A

  DSC Alarm Debug                 Zone number 3 Closed.
  DSC Alarm Debug                 RX: 6100042B

  DSC Alarm Debug                 Zone number 4 Closed.
  DSC Alarm Debug                 RX: 6100052C

  DSC Alarm Debug                 Zone number 5 Closed.
  DSC Alarm Debug                 RX: 6100062D

  DSC Alarm Debug                 Zone number 6 Closed.
  DSC Alarm Debug                 RX: 6100072E

  DSC Alarm Debug                 Zone number 7 Closed.
  DSC Alarm Debug                 RX: 6100082F

  DSC Alarm Debug                 Zone number 8 Closed.
  DSC Alarm Debug                 RX: 61000930

  DSC Alarm Debug                 Zone number 9 Closed.
  DSC Alarm Debug                 RX: 61001028

  DSC Alarm Debug                 Zone number 10 Closed.
  DSC Alarm Debug                 RX: 60901131

  DSC Alarm Debug                 Zone number 11 Open.
  DSC Alarm Debug                 RX: 6100122A

  DSC Alarm Debug                 Zone number 12 Closed.
  DSC Alarm Debug                 RX: 6100132B

  DSC Alarm Debug                 Zone number 13 Closed.
  DSC Alarm Debug                 RX: 6100142C

  DSC Alarm Debug                 Zone number 14 Closed.
  DSC Alarm Debug                 RX: 6100152D

  DSC Alarm Debug                 Zone number 15 Closed.
  DSC Alarm Debug                 RX: 6100162E

  DSC Alarm Debug                 Zone number 16 Closed.
  DSC Alarm Debug                 RX: 6100172F

  DSC Alarm Debug                 Zone number 17 Closed.
  DSC Alarm Debug                 RX: 61001830

  DSC Alarm Debug                 Zone number 18 Closed.
  DSC Alarm Debug                 RX: 61001931

  DSC Alarm Debug                 Zone number 19 Closed.
  DSC Alarm Debug                 RX: 61002029

  DSC Alarm Debug                 Zone number 20 Closed.
  DSC Alarm Debug                 RX: 6100212A

  DSC Alarm Debug                 Zone number 21 Closed.
  DSC Alarm Debug                 RX: 6100222B

  DSC Alarm Debug                 Zone number 22 Closed.
  DSC Alarm Debug                 RX: 6100232C

  DSC Alarm Debug                 Zone number 23 Closed.
  DSC Alarm Debug                 RX: 6100242D

  DSC Alarm Debug                 Zone number 24 Closed.
  DSC Alarm Debug                 RX: 6100252E

  DSC Alarm Debug                 Zone number 25 Closed.
  DSC Alarm Debug                 RX: 6100262F

  DSC Alarm Debug                 Zone number 26 Closed.
  DSC Alarm Debug                 RX: 61002730

  DSC Alarm Debug                 Zone number 27 Closed.
  DSC Alarm Debug                 RX: 61002831

  DSC Alarm Debug                 Zone number 28 Closed.
  DSC Alarm Debug                 RX: 61002932

  DSC Alarm Debug                 Zone number 29 Closed.
  DSC Alarm Debug                 RX: 6100302A

  DSC Alarm Debug                 Zone number 30 Closed.
  DSC Alarm Debug                 RX: 6100312B

  DSC Alarm Debug                 Zone number 31 Closed.
  DSC Alarm Debug                 RX: 6100322C

  DSC Alarm Debug                 Zone number 32 Closed.
  DSC Alarm Debug                 RX: 6100332D

  DSC Alarm Debug                 Zone number 33 Closed.
  DSC Alarm Debug                 RX: 6100342E

  DSC Alarm Debug                 Zone number 34 Closed.
  DSC Alarm Debug                 RX: 6100352F

  DSC Alarm Debug                 Zone number 35 Closed.
  DSC Alarm Debug                 RX: 61003630

  DSC Alarm Debug                 Zone number 36 Closed.
  DSC Alarm Debug                 RX: 61003731

  DSC Alarm Debug                 Zone number 37 Closed.
  DSC Alarm Debug                 RX: 61003832

  DSC Alarm Debug                 Zone number 38 Closed.
  DSC Alarm Debug                 RX: 61003933

  DSC Alarm Debug                 Zone number 39 Closed.
  DSC Alarm Debug                 RX: 6100402B

  DSC Alarm Debug                 Zone number 40 Closed.
  DSC Alarm Debug                 RX: 6100412C

  DSC Alarm Debug                 Zone number 41 Closed.
  DSC Alarm Debug                 RX: 6100422D

  DSC Alarm Debug                 Zone number 42 Closed.
  DSC Alarm Debug                 RX: 6100432E

  DSC Alarm Debug                 Zone number 43 Closed.
  DSC Alarm Debug                 RX: 6100442F

  DSC Alarm Debug                 Zone number 44 Closed.
  DSC Alarm Debug                 RX: 61004530

  DSC Alarm Debug                 Zone number 45 Closed.
  DSC Alarm Debug                 RX: 61004631

  DSC Alarm Debug                 Zone number 46 Closed.
  DSC Alarm Debug                 RX: 61004732

  DSC Alarm Debug                 Zone number 47 Closed.
  DSC Alarm Debug                 RX: 61004833

  DSC Alarm Debug                 Zone number 48 Closed.
  DSC Alarm Debug                 RX: 61004934

  DSC Alarm Debug                 Zone number 49 Closed.
  DSC Alarm Debug                 RX: 6100502C

  DSC Alarm Debug                 Zone number 50 Closed.
  DSC Alarm Debug                 RX: 6100512D

  DSC Alarm Debug                 Zone number 51 Closed.
  DSC Alarm Debug                 RX: 6100522E

  DSC Alarm Debug                 Zone number 52 Closed.
  DSC Alarm Debug                 RX: 6100532F

  DSC Alarm Debug                 Zone number 53 Closed.
  DSC Alarm Debug                 RX: 61005430

  DSC Alarm Debug                 Zone number 54 Closed.
  DSC Alarm Debug                 RX: 61005531

  DSC Alarm Debug                 Zone number 55 Closed.
  DSC Alarm Debug                 RX: 61005632

  DSC Alarm Debug                 Zone number 56 Closed.
  DSC Alarm Debug                 RX: 61005733

  DSC Alarm Debug                 Zone number 57 Closed.
  DSC Alarm Debug                 RX: 61005834

  DSC Alarm Debug                 Zone number 58 Closed.
  DSC Alarm Debug                 RX: 61005935

  DSC Alarm Debug                 Zone number 59 Closed.
  DSC Alarm Debug                 RX: 6100602D

  DSC Alarm Debug                 Zone number 60 Closed.
  DSC Alarm Debug                 RX: 6100612E

  DSC Alarm Debug                 Zone number 61 Closed.
  DSC Alarm Debug                 RX: 6100622F

  DSC Alarm Debug                 Zone number 62 Closed.
  DSC Alarm Debug                 RX: 61006330

  DSC Alarm Debug                 Zone number 63 Closed.
  DSC Alarm Debug                 RX: 61006431

  DSC Alarm Debug                 Zone number 64 Closed.
  Received INSTEON                "Thermostat" temperature changed to 76.0
  DSC Alarm Error                 Error in plugin execution runConcurrentThread:

Traceback (most recent call last):
  File "plugin.py", line 84, in runConcurrentThread
  File "/Library/Application Support/Perceptive Automation/Indigo 5/Plugins/DSC Alarm.indigoPlugin/Contents/Server Plugin/DSC.py", line 491, in startComm
  File "/Library/Application Support/Perceptive Automation/Indigo 5/Plugins/DSC Alarm.indigoPlugin/Contents/Server Plugin/DSC.py", line 112, in readPacket
<type 'exceptions.UnicodeDecodeError'>: 'ascii' codec can't decode byte 0xdf in position 15: ordinal not in range(128)

  DSC Alarm Error                 plugin runConcurrentThread function returned or failed; will attempt again in 10 seconds
  DSC Alarm Debug                 runConcurrentThread called
  DSC Alarm Debug                 startComm called

Jun 27, 2011 5:48:19 PM
  Schedule                        Alarm_Front Door Closed (delayed action)
  Schedule                        Alarm_Kitchen Door Closed (delayed action)
  Schedule                        Alarm_Basement Door Closed (delayed action)
  Schedule                        Alarm_Dining Room Motion Off (delayed action)
  Schedule                        Alarm_HallWay Motion Off (delayed action)
  Schedule                        Alarm_Laundry Motion Off (delayed action)
  Schedule                        Alarm_Basements living room Motion Off (delayed action)
  Schedule                        Alarm_Play Room Motion Off (delayed action)
  Schedule                        Alarm_Garage Rear Door Closed (delayed action)
  Schedule                        Alarm_Garage Right Door Closed (delayed action)
  Schedule                        Alarm_Office Motion Off (delayed action)

Jun 27, 2011 5:48:45 PM
  Received INSTEON                "Thermostat" humidity changed to 50.0
  DSC Alarm Debug                 RX: 561107569

  DSC Alarm Debug                 Cmd:561 Dat:1075 Sum:105
  DSC Alarm Debug                 RX: 56210796E

  DSC Alarm Debug                 Cmd:562 Dat:1079 Sum:110
  DSC Alarm Error                 Error in plugin execution runConcurrentThread:

Traceback (most recent call last):
  File "plugin.py", line 84, in runConcurrentThread
  File "/Library/Application Support/Perceptive Automation/Indigo 5/Plugins/DSC Alarm.indigoPlugin/Contents/Server Plugin/DSC.py", line 491, in startComm
  File "/Library/Application Support/Perceptive Automation/Indigo 5/Plugins/DSC Alarm.indigoPlugin/Contents/Server Plugin/DSC.py", line 112, in readPacket
<type 'exceptions.UnicodeDecodeError'>: 'ascii' codec can't decode byte 0xdf in position 15: ordinal not in range(128)

  DSC Alarm Error                 plugin runConcurrentThread function returned or failed; will attempt again in 10 seconds
  DSC Alarm Debug                 runConcurrentThread called
  DSC Alarm Debug                 startComm called

Jun 27, 2011 5:49:51 PM
  DSC Alarm Error                 Error in plugin execution runConcurrentThread:

Traceback (most recent call last):
  File "plugin.py", line 84, in runConcurrentThread
  File "/Library/Application Support/Perceptive Automation/Indigo 5/Plugins/DSC Alarm.indigoPlugin/Contents/Server Plugin/DSC.py", line 491, in startComm
  File "/Library/Application Support/Perceptive Automation/Indigo 5/Plugins/DSC Alarm.indigoPlugin/Contents/Server Plugin/DSC.py", line 112, in readPacket
<type 'exceptions.UnicodeDecodeError'>: 'ascii' codec can't decode byte 0xdf in position 15: ordinal not in range(128)

  DSC Alarm Error                 plugin runConcurrentThread function returned or failed; will attempt again in 10 seconds
  DSC Alarm Debug                 runConcurrentThread called
  DSC Alarm Debug                 startComm called



This is from the DSC Script i'v bin using see if it helps.

{"000 Poll", "001 Status Request", "002 Labels Request", "010 Set Time and Date", "020 Command Output Control", "030 Partition Arm Control Away", "031 Partition Arm Contro Say-Arm", "032 Partition Arm Contro Zero Entry Delay", "033 Partition Arm Contro With Code", "040 Partition Disarm Control", "050 Descriptive Arming Control", "055 Time Stamp Contril", "056 Time/Date Broadcast Control", "057 Temperature Broadcast Control", "058 Virtual Keypad Control (Virt)", "060 Trigger Panic Alarm", "070 Key Pressed (Virt)", "080 Baud Rate Change", "095 Get Temprerature Set Point", "096 Temperature Change", "097 Save Temperature Setting", "100 Bypass Zone Control", "101 Unbypass Zone Control", "200 Code Send", "500 Command Acknowledge", "501 Command Error", "502 System Error", "550 Time/Date Broadcast", "560 Ring Detected", "561 Indoor Temperature Broadcast", "562 Outdoor Temperature Broadcast", "563 Thrmostat Set Points", "570 Broadcast Labels", "580 Baud Rate Set", "601 Zone Alarm", "602 Zone Restoral", "603 Zone Tamper", "604 Zone Tamper Restoral", "605 Zone Fault", "606 Zone Fault Restoral", "609 Zone Opened", "610 Zone Restored", "620 Duress Alarm", "621 [F] Key Alarm", "622 [F] Key Restoral", "623 [A] Key Alarm", "624 [A] Key Restoral", "625 [P] Key Alarm", "626 Partition Ready", "627 Door Forced Alarm", "628 Door Forced Restore", "629 Door Open Too Long Alarm", "630 Door Open Too Long Restore", "631 Auxiliary Input  Alarm", "632 Auxiliary Input  Alarm  Restore", "633 Waterflow Alarm", "634 Waterflow Restore", "635 2 Wire Smoke Trouble", "636 2 Wire Smoke Trouble Restore", "637 Waterflow Trouble", "638 Waterflow Trouble Restore", "650 Partition Ready", "651 Partition Not Ready", "652 Partition Armed", "653 Partition Force Armed", "654 Partition In Alarm", "655 Partition Disarm", "656 Exit Delay in Progress", "657 Entry Delay in Progress", "658 Keypad Lock-out", "659 Keypad Blanking", "660 Command Output In Progress", "670 Invalid Access Code", "671 Function Not Available", "672 Fail to Arm", "673 Partition Busy", "700 User Closing", "701 Special Closing", "702 Partial Closing", "750 User Opening", "751 Special Opening", "800 Panel Battery Trouble", "801 Panel Battery Restoral", "802 Panel AC Trouble", "803 Panel AC Restoral", "804 Panel Aux Trouble", "805 Panel Aux Restoral", "806 System Bell Trouble", "807 System Bell Restoral", "808 Combus Trouble", "809 Combus Restoral", "810 TLM Failure", "811 TLM Restoral", "812 TLM Failure Line 2", "813 TLM Restoral Line 2", "814 FTC Trouble", "815 FTC Restoral", "816 Buffer Near Full", "817 Ground Fault", "818 Ground Fault Restoral", "819 General System Trouble", "820 General System Trouble Restoral", "821 General Device Low Battery", "822 General Device Low Battery Restoral", "823 General Module Com Fault", "824 General Module Com Fault Restoral", "825 Wireless Key Low Battery Alarm", "826 Wireless Key Low Battery Restoral", "827 Handheld Keypad Low Battery Alarm", "828 Handheld Keypad Low Battery Restoral", "829 General System Tamper Alarm", "830 General System Tamper Restore", "831 Home Automation Trouble", "832 Home Automation Trouble Restore", "840 Trouble Status", "841 Trouble Status Restore", "842 Fire Trouble Alarm", "843 Fire Trouble Alarm Restore", "900 Code Required", "901 LCD Update", "902 LCD Cursor", "903 LED Status", "904 Beep Status", "905 Tone Status", "906 Buzzer Status", "907 Door Chime Status", "908 Software Version"}

Posted on
Mon Jun 27, 2011 4:43 pm
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

I got the info I needed. There's a glitch in the LCD message parsing. I'll have it fixed soon.

Travis

Posted on
Mon Jun 27, 2011 10:26 pm
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

Version 0.9.1 released:
- The LCD error should be fixed.
- Support for DSC temperature sensors has also been added.

Download the plugin again from the original post.

Posted on
Tue Jun 28, 2011 5:35 am
Korey offline
User avatar
Posts: 813
Joined: Jun 04, 2008
Location: Henderson, NV

Re: DSC Alarm Plugin

travisc wrote:
Version 0.9.1 released:
- The LCD error should be fixed.
- Support for DSC temperature sensors has also been added.

Download the plugin again from the original post.



Now... I need to get a DSC alarm.. :shock:

Thanks Travis, Very impressive how quick you whip up plugins!

--
Korey

Posted on
Tue Jun 28, 2011 10:13 am
jay (support) offline
Site Admin
User avatar
Posts: 18220
Joined: Mar 19, 2008
Location: Austin, Texas

Re: DSC Alarm Plugin

+1 Korey

Was just thinking to myself I need to check in to how much it would cost to replace my NS8 with a DSC panel... :D

Extremely cool Travis - thanks a ton for the contributions (you've nicely illustrated exactly why we wanted to spend so much time getting the plugin API right). Once you feel they're ready for primetime, feel free to post them in the File Library where it will be easier for people to find. You can point back to their respective threads or create new user-oriented (non-development) threads in the User Contributions forum.

Jay (Indigo Support)
Twitter | Facebook | LinkedIn

Posted on
Tue Jun 28, 2011 11:04 am
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

jay wrote:
+1 Korey

Was just thinking to myself I need to check in to how much it would cost to replace my NS8 with a DSC panel... :D

Extremely cool Travis - thanks a ton for the contributions (you've nicely illustrated exactly why we wanted to spend so much time getting the plugin API right). Once you feel they're ready for primetime, feel free to post them in the File Library where it will be easier for people to find. You can point back to their respective threads or create new user-oriented (non-development) threads in the User Contributions forum.


Thanks Jay! Now that I've gotten the hang of Python, developing these plugins has been quite enjoyable. You guys have done a great job on the API.

Actually I have a question or two for you Jay. The alarm zones and alarm keypad devices this plugin uses are custom devices. Indigo doesn't show a state for them in the device list, it lists them in the box below the window. Which makes sense, because there are multiple states, which one would it show. Is there a way to make one of the states the default state that Indigo will show in the Device List?

Also, the custom devices don't seem to have the option of being shown remotely. I'm pretty sure I understand why, there are so many variables at play here, each plugin would want different states to be displayed, it would be tricky to implement. Just wondering if I'm doing something wrong or if this is something that will be added in time.

After a bit of testing I'll definitely post these in the library and create a different thread.

Thanks again, great work! :D

Posted on
Tue Jun 28, 2011 11:09 am
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

I've also received a request for the ability to trigger different events based on which alarm user arms/disarms the alarm. I'll get that added shortly as well.

If anyone has the PC-5401 interface board it'd be great if you can test this plugin with it and report back. So far I believe it's only been tested with the IT-100.

Posted on
Tue Jun 28, 2011 11:27 am
jay (support) offline
Site Admin
User avatar
Posts: 18220
Joined: Mar 19, 2008
Location: Austin, Texas

Re: DSC Alarm Plugin

travisc wrote:
Actually I have a question or two for you Jay. The alarm zones and alarm keypad devices this plugin uses are custom devices. Indigo doesn't show a state for them in the device list, it lists them in the box below the window. Which makes sense, because there are multiple states, which one would it show. Is there a way to make one of the states the default state that Indigo will show in the Device List?


Yep - add this to your <Device> element in Devices.xml:

Code: Select all
<UiDisplayStateId>stateIdHere</UiDisplayStateId>


with the right state ID and that state will be shown in the "State" column of the device table.

travisc wrote:
Also, the custom devices don't seem to have the option of being shown remotely. I'm pretty sure I understand why, there are so many variables at play here, each plugin would want different states to be displayed, it would be tricky to implement. Just wondering if I'm doing something wrong or if this is something that will be added in time.


We're still noodling how to make remote custom device UI's work. The problem is not only what state data to show (and how), but what controls (if any) we show, how to specify the UI (if any), etc. - lots of unknowns. We may not get it working for GM - it just depends on what we come up with, how much time it will take to implement, and whether we can get something in for Indigo Touch without a code change.

Jay (Indigo Support)
Twitter | Facebook | LinkedIn

Posted on
Tue Jun 28, 2011 12:28 pm
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

jay wrote:
Yep - add this to your <Device> element in Devices.xml:

Perfect. Thanks!

jay wrote:
We're still noodling how to make remote custom device UI's work. The problem is not only what state data to show (and how), but what controls (if any) we show, how to specify the UI (if any), etc. - lots of unknowns. We may not get it working for GM - it just depends on what we come up with, how much time it will take to implement, and whether we can get something in for Indigo Touch without a code change.

Understood. It's really not that big of a deal. I'd definitely vote for the ability to use device states in the condition editor over this. :D

Thanks

Posted on
Tue Jun 28, 2011 1:14 pm
peppop offline
User avatar
Posts: 104
Joined: Oct 18, 2006
Location: Mas

Re: DSC Alarm Plugin

This is an excellent plugin, its well don, works great.
I was wondering if you can add a few things to the keypad?
You have Armand stay, arming away, and Disarm. Can you add panic alarm, fire alarm, and medical.
And can you add key-presses, that would be great, 1-0 *, #, to be able to create a virtual keyboard thanks again.

Posted on
Tue Jun 28, 2011 2:49 pm
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

peppop wrote:
This is an excellent plugin, its well don, works great.

Thanks. :)

peppop wrote:
I was wondering if you can add a few things to the keypad?
You have Armand stay, arming away, and Disarm. Can you add panic alarm, fire alarm, and medical.
And can you add key-presses, that would be great, 1-0 *, #, to be able to create a virtual keyboard thanks again.

Yes that shouldn't be too hard. If you've used this before in the Applescript version, did you find you had to send the "Virtual Keypad Control On" command (058) before you could start sending key presses (cmd 070)?

Posted on
Tue Jun 28, 2011 3:06 pm
peppop offline
User avatar
Posts: 104
Joined: Oct 18, 2006
Location: Mas

Re: DSC Alarm Plugin

Yes that shouldn't be too hard. If you've used this before in the Applescript version, did you find you had to send the "Virtual Keypad Control On" command (058) before you could start sending key presses (cmd 070)?



No I think Virtual Keypad is on by default.
This is wat I wood send.
press - 1
Code: Select all
property connectionName : "DSCT100"
tell application "Serial Bridge.app"
   «event SRBRSdDt» connectionName given «class SnBL»:{48, 55, 48, 49, 67, 56, 13, 10}
   «event SRBRSdDt» connectionName given «class SnBL»:{48, 55, 48, 94, 70, 53, 13, 10}
end tell


Panic Alarm
Code: Select all
property connectionName : "DSC T-100"
tell application "Serial Bridge.app"
   «event SRBRSdDt» connectionName given «class SnBL»:{48, 54, 48, 51, 67, 57, 13, 10}
end tell


Press- <
Code: Select all
property connectionName : "DSCT100"
tell application "Serial Bridge.app"
   «event SRBRSdDt» connectionName given «class SnBL»:{48, 55, 48, 60, 68, 51, 13, 10}
   «event SRBRSdDt» connectionName given «class SnBL»:{48, 55, 48, 94, 70, 53, 13, 10}
end tell



Get Tempe Set Point
Code: Select all
property connectionName : "DSCT100"
tell application "Serial Bridge.app"
   «event SRBRSdDt» connectionName given «class SnBL»:{48, 57, 53, 49, 67, 70, 13, 10}
end tell


And so on...

Posted on
Tue Jun 28, 2011 9:10 pm
travisc offline
User avatar
Posts: 346
Joined: Sep 07, 2010
Location: Toronto, Canada

Re: DSC Alarm Plugin

Version 0.9.3 released:
- Device states now show up properly in the Device List. Unfortunately existing devices have to be deleted and recreated for this fix to take effect.
- Added ability to trigger Fire, Medical, and Panic alarms.
- Added ability to send keypad key presses or even key strings.
- Added events that trigger when the alarm is armed or disarmed by a particular user.

Posted on
Wed Jun 29, 2011 12:10 pm
peppop offline
User avatar
Posts: 104
Joined: Oct 18, 2006
Location: Mas

Re: DSC Alarm Plugin

Works Great!!!!.
You can even program the alarm with it.
Now if we could just get Jay ore Matt to add button sounds on control pages in Indigo.

Image


Image

Posted on
Wed Jul 06, 2011 1:54 am
paulretlas offline
Posts: 3
Joined: Jul 06, 2011

Re: DSC Alarm Plugin

Bit of a noob, hoping to get steered the right way.

Having a DSC1832 installed and the installer told me a TL-250 comes with it. Will this work module work? I was unclear after reading that other poster's comment.

Also, has the "Stay" feature been fixed for the TL-150/250?

Thanks for the hard work!