Posted on
Tue Apr 28, 2015 2:26 pm
Unklmarty offline
User avatar
Posts: 59
Joined: Jun 30, 2006
Location: NJ

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

Whew I almost had a heart attack! but I might have located the source of the error.
The computer or server running Indigo was running 6.1, the remote computer or client I was accessing the server from and trying to edit devices was running 6.0.1.
On the remote computer running 6.0.1 when I checked to see if it needed an upgrade, a box poped up claiming "No updates available". Seeing that the Server version was running 6.1 and the Client version was running 6.0.1, I decided to update the client computer to 6.1. After updating Indigo on the client computer to 6.1, I now can edit all devices.
Not sure why the software reported no updated available on the client computer running 6.0.1.
Now if I can only get the water sensors to stop sending multiple heartbeats I could relax.
m

Posted on
Tue Apr 28, 2015 2:29 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

Unklmarty wrote:
Not sure why the software reported no updated available on the client computer running 6.0.1.

You're not the first to experience this.

Matt, I know you expect people to upgrade clients at the same time, and check-for-updates is a server side process, but could we suggest a feature request for the Client to report that the server it's connected to is newer than itself and might experience problems?

Peter

Posted on
Tue Apr 28, 2015 5:57 pm
jay (support) offline
Site Admin
User avatar
Posts: 18199
Joined: Mar 19, 2008
Location: Austin, Texas

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

We have a flag that we usually flip so that the client will show an error when connecting to an incompatible server. Unfortunately, we forgot to flip that switch in the 6.1.0 release... :cry:

Jay (Indigo Support)
Twitter | Facebook | LinkedIn

Posted on
Wed Apr 29, 2015 11:55 am
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

Hehe!

Posted on
Fri Mar 18, 2016 2:38 am
moyse offline
Posts: 39
Joined: Apr 14, 2014

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

Anyone had a problem like this ... if I switch this off and on at the wall, Indigo gets updated (i.e. I can see if the switch is on). A sync sometimes works. But switching it off/on from within indigo never works (at least, not the last 20 or so attempts).

Here's a log file where I try to turn it off from indigo (which fails), then turn it off manually (the status change is received), then sync it (which works ... though honestly I'm a bit surprised it claims to have device 1 as a neighbour ... that seems very unlikely), and then I try to turn it on remotely (which fails).

I'm a bit baffled!

Ed

18 Mar 2016 09:27:07
Z-Wave Debug SENT setMultiLevelValue: 01 0A 00 13 14 03 26 01 00 05 1C CF
Z-Wave Debug RCVD setMultiLevelValue: 01 05 00 13 1C 01 F4 (node NAK)
Z-Wave Error send "Back door light - Micro Smart Energy Illuminator (DSC19)" off failed
Z-Wave Debug RCVD requestBinarySensorStatus: 01 09 00 04 00 1D 03 30 03 FF 20
Z-Wave Debug . . requestBinarySensorStatus: node 029, endpoint None, value 255
Z-Wave received "Living room" status update is on
Z-Wave Debug RCVD sensorSetLevel: 01 09 00 04 00 1D 03 20 01 FF 32
Z-Wave Debug . . sensorSetLevel: node 029, endpoint None, cmdClass 20, value 255
Z-Wave Debug filtering duplicate command -- old: 30, 0, FF, new: 20, 0, FF (0.5369 secs)
Z-Wave Debug RCVD dimmerSetLevel: 01 09 00 04 00 14 03 20 03 00 C6
Z-Wave Debug . . dimmerSetLevel: node 020, endpoint None, value 0
Z-Wave received "Back door light - Micro Smart Energy Illuminator (DSC19)" status update is off
Z-Wave Debug queueing request of "020 - Back door light - Micro Smart Energy Illuminator (DSC19)" (activity detected)
Z-Wave Debug polling status of node "020 - Back door light - Micro Smart Energy Illuminator (DSC19)" (post-activity list)
Z-Wave Debug SENT requestMeterLevel: 01 0A 00 13 14 03 32 01 00 05 1D DA
Z-Wave Debug RCVD requestMeterLevel: 01 14 00 04 00 14 0E 32 02 21 64 00 00 3D 94 00 81 00 00 3D 92 07
Z-Wave Debug . . requestMeterLevel: node 020, endpoint None, meterType 01, raw value 6400...
Z-Wave Debug . . requestMeterLevel: 15.764 kWh (float: 15.764000)
Z-Wave received "Back door light - Micro Smart Energy Illuminator (DSC19)" energy total to 15.764 kWh
Z-Wave Debug SENT requestMeterLevel: 01 0A 00 13 14 03 32 01 10 05 1E C9
Z-Wave Debug RCVD requestMeterLevel: 01 14 00 04 00 14 0E 32 02 21 74 00 00 00 00 00 00 00 00 00 00 90
Z-Wave Debug . . requestMeterLevel: node 020, endpoint None, meterType 01, raw value 7400...
Z-Wave Debug . . requestMeterLevel: 0.000 W (float: 0.000000)
Z-Wave Debug intiatingSyncUI (timeout in 300 seconds)
Z-Wave Syncing - started for "Back door light - Micro Smart Energy Illuminator (DSC19)"
Z-Wave Debug SENT getNodeNeighbors: 01 06 00 80 14 01 01 6D
Z-Wave Debug RCVD getNodeNeighbors: 01 20 01 80 81 02 00 20 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 FD
Z-Wave Debug . . getNodeNeighbors: nodeId 020, neighbors: 1, 8, 10, 30
Z-Wave Syncing - retrieved module neighbors list: 1, 8, 10, 30
Z-Wave Syncing - assigning return route to "020 - Back door light - Micro Smart Energy Illuminator (DSC19)"
Z-Wave Debug SENT assignReturnRoute: 01 05 00 46 14 01 A9
Z-Wave Debug RCVD assignReturnRoute: 01 04 01 46 01 BD
Z-Wave Debug RCVD assignReturnRoute: 01 05 00 46 01 00 BD
Z-Wave Debug . . assignReturnRoute: node 020, success 1
Z-Wave Syncing - assigned return route
Z-Wave Debug SENT requestNodeInfo: 01 06 00 60 14 04 1F 96
Z-Wave Debug RCVD nodeInfoFrame: 01 14 00 49 84 14 0E 04 11 04 26 32 27 2C 2B 70 85 72 86 EF 82 75
Z-Wave Debug . . nodeInfoFrame: node 020, combined class list: 20v1 70v1 72v1 85v1 26v1 27v1 2Bv1 2Cv1 32v1 86v1
Z-Wave Debug SENT requestManufactureInfo: 01 09 00 13 14 02 72 04 05 20 A0
Z-Wave Debug RCVD requestManufactureInfo: 01 0E 00 04 00 14 08 72 05 00 86 00 03 00 13 08
Z-Wave Debug . . requestManufactureInfo: node 020, manufacturerId 0086, productId 00030013
Z-Wave Debug . . requestManufactureInfo: Aeon Labs, Micro Smart Energy Illuminator (DSC19)
Z-Wave Syncing - retrieved manufacture and model names: Aeon Labs - 0086, Micro Smart Energy Illuminator (DSC19) - 00030013
Z-Wave Debug SENT requestVersInfoGen: 01 09 00 13 14 02 86 11 05 21 40
Z-Wave Debug RCVD requestVersInfoGen: 01 0D 00 04 00 14 07 86 12 03 03 28 01 0F 57
Z-Wave Debug . . requestVersInfoGen: node 020, protoVers 3.40, appVers 1.15
Z-Wave Syncing - retrieved protocol version 3.40, app version 1.15
Z-Wave Debug SENT requestVersInfoCmdClass: 01 0A 00 13 14 03 86 13 26 05 22 65
Z-Wave Debug RCVD requestVersInfoCmdClass: 01 0A 00 04 00 14 04 86 14 26 02 57
Z-Wave Debug . . requestVersInfoCmdClass: node 020, class command 26 using version 2
Z-Wave Debug . . requestVersInfoCmdClass: node 020, combined class list: 20v1 70v1 72v1 85v1 26v2 27v1 2Bv1 2Cv1 32v1 86v1
Z-Wave Debug SENT requestVersInfoCmdClass: 01 0A 00 13 14 03 86 13 32 05 23 70
Z-Wave Debug RCVD requestVersInfoCmdClass: 01 0A 00 04 00 14 04 86 14 32 03 42
Z-Wave Debug . . requestVersInfoCmdClass: node 020, class command 32 using version 3
Z-Wave Debug . . requestVersInfoCmdClass: node 020, combined class list: 20v1 70v1 72v1 85v1 26v2 27v1 2Bv1 2Cv1 32v3 86v1
Z-Wave Syncing - retrieved class hierarchy: Routing Slave : Mulitlevel Switch : Dimmable Scene Switch (04 : 11 : 04, base 26)
Z-Wave Syncing - retrieved command classes: 20v1 70v1 72v1 85v1 26v2 27v1 2Bv1 2Cv1 32v3 86v1
Z-Wave Debug SENT requestAssociationGroupCount: 01 09 00 13 14 02 85 05 05 24 52
Z-Wave Debug RCVD requestAssociationGroupCount: 01 09 00 04 00 14 03 85 06 01 67
Z-Wave Debug . . requestAssociationGroupCount: node 020, group count: 1
Z-Wave Debug SENT requestAssociations: 01 0A 00 13 14 03 85 02 01 05 25 57
Z-Wave Debug RCVD requestAssociations: 01 0C 00 04 00 14 06 85 03 01 05 00 01 66
Z-Wave Debug . . requestAssociations: node 020, group: 1, num associations: 1, max associations: 5, replies left: 0
Z-Wave Debug . . requestAssociations: node 020, group: 1, associations: [1]
Z-Wave Syncing - retrieved group 1 associations: [1]
Z-Wave Syncing - group 1 association to interface already exists (skipping)
Z-Wave Debug SENT requestMeterInfo: 01 09 00 13 14 02 32 03 05 26 E1
Z-Wave Debug RCVD requestMeterInfo: 01 0A 00 04 00 14 04 32 04 81 35 63
Z-Wave Debug . . requestMeterInfo: node 020, meterType 01, subTypeFlags 35, supportsReset True
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 01 05 27 A7
Z-Wave Debug module failed to reply to request (non-fatal, skipping request)
Z-Wave Syncing - failed to retrieve parameter 1 "Report status as volts" (skipping)
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 50 05 28 F9
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 50 01 02 00 00 00 CC
Z-Wave Debug . . requestConfigVal: node 020, parm index 80, value 2 (size 1)
Z-Wave Syncing - retrieved parameter 80 "Automatic notification" is 2
Z-Wave Debug SENT setConfigVal: 01 0C 00 13 14 05 70 04 50 01 02 05 29 FA
Z-Wave Syncing - device "020 - Back door light - Micro Smart Energy Illuminator (DSC19)" parameter 80 "Automatic notification" changed to 2 (was 2)
Z-Wave Debug . . pushNewValToNode: node 020, combined config vals: 80:2
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 5A 05 2A F1
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 5A 01 00 00 00 00 C4
Z-Wave Debug . . requestConfigVal: node 020, parm index 90, value 0 (size 1)
Z-Wave Syncing - retrieved parameter 90 "Enable energy change reports" is false
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 90:0
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 5B 05 2B F1
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 5B 02 00 32 00 00 F4
Z-Wave Debug . . requestConfigVal: node 020, parm index 91, value 50 (size 2)
Z-Wave Syncing - retrieved parameter 91 "Report threshold watts" is 50 watts
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 90:0 91:50
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 5C 05 2C F1
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 5C 01 0A 00 00 00 C8
Z-Wave Debug . . requestConfigVal: node 020, parm index 92, value 10 (size 1)
Z-Wave Syncing - retrieved parameter 92 "Report threshold percentage" is 10 %
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 90:0 91:50 92:10
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 65 05 2D C9
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 65 04 00 00 00 00 FE
Z-Wave Debug . . requestConfigVal: node 020, parm index 101, value 0 (size 4)
Z-Wave Syncing - retrieved parameter 101 "Group 1 report sent flags" is 0
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 90:0 91:50 92:10 101:0
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 66 05 2E C9
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 66 04 00 00 00 00 FD
Z-Wave Debug . . requestConfigVal: node 020, parm index 102, value 0 (size 4)
Z-Wave Syncing - retrieved parameter 102 "Group 2 report sent flags" is 0
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 101:0 102:0 90:0 91:50 92:10
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 67 05 2F C9
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 67 04 00 00 00 00 FC
Z-Wave Debug . . requestConfigVal: node 020, parm index 103, value 0 (size 4)
Z-Wave Syncing - retrieved parameter 103 "Group 3 report sent flags" is 0
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 101:0 102:0 103:0 90:0 91:50 92:10
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 6F 05 30 DE
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 6F 04 00 00 02 58 AE
Z-Wave Debug . . requestConfigVal: node 020, parm index 111, value 600 (size 4)
Z-Wave Syncing - retrieved parameter 111 "Delay between reporting energy values" is 600 seconds
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 101:0 102:0 103:0 90:0 91:50 92:10 111:600
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 70 05 31 C0
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 70 04 00 00 02 58 B1
Z-Wave Debug . . requestConfigVal: node 020, parm index 112, value 600 (size 4)
Z-Wave Syncing - retrieved parameter 112 "Delay between reporting for group 2 (unused)" is 600 seconds
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 112:600 101:0 102:0 103:0 90:0 91:50 92:10 111:600
Z-Wave Debug SENT requestConfigVal: 01 0A 00 13 14 03 70 05 71 05 32 C2
Z-Wave Debug RCVD requestConfigVal: 01 0E 00 04 00 14 08 70 06 71 04 00 00 02 58 B0
Z-Wave Debug . . requestConfigVal: node 020, parm index 113, value 600 (size 4)
Z-Wave Syncing - retrieved parameter 113 "Delay between reporting for group 3 (unused)" is 600 seconds
Z-Wave Debug . . requestConfigVal: node 020, combined config vals: 80:2 112:600 113:600 101:0 102:0 103:0 90:0 91:50 92:10 111:600
Z-Wave Syncing - complete
Z-Wave Debug stopped polling of "020 - Back door light - Micro Smart Energy Illuminator (DSC19)"
Z-Wave Debug started polling of "020 - Back door light - Micro Smart Energy Illuminator (DSC19)" approx every 3600 seconds
Z-Wave Debug SENT requestDimmerStatus: 01 09 00 13 14 02 26 02 05 33 E1
Z-Wave sent "Back door light - Micro Smart Energy Illuminator (DSC19)" status request
Z-Wave sent "Back door light - Micro Smart Energy Illuminator (DSC19)" energy status request
Z-Wave Debug RCVD requestDimmerStatus: 01 09 00 04 00 14 03 26 03 00 C0
Z-Wave Debug . . requestDimmerStatus: node 020, endpoint None, value 0
Z-Wave Debug SENT requestMeterLevel: 01 0A 00 13 14 03 32 01 00 05 34 F3
Z-Wave Debug RCVD requestMeterLevel: 01 14 00 04 00 14 0E 32 02 21 64 00 00 3D 94 00 1A 00 00 3D 94 9A
Z-Wave Debug . . requestMeterLevel: node 020, endpoint None, meterType 01, raw value 6400...
Z-Wave Debug . . requestMeterLevel: 15.764 kWh (float: 15.764000)
Z-Wave Debug SENT requestMeterLevel: 01 0A 00 13 14 03 32 01 10 05 35 E2
Z-Wave Debug RCVD requestMeterLevel: 01 14 00 04 00 14 0E 32 02 21 74 00 00 00 00 00 00 00 00 00 00 90
Z-Wave Debug . . requestMeterLevel: node 020, endpoint None, meterType 01, raw value 7400...
Z-Wave Debug . . requestMeterLevel: 0.000 W (float: 0.000000)
Z-Wave Debug RCVD requestBinarySensorStatus: 01 09 00 04 00 1D 03 30 03 00 DF
Z-Wave Debug . . requestBinarySensorStatus: node 029, endpoint None, value 0
Z-Wave received "Living room" status update is off
Z-Wave Debug RCVD sensorSetLevel: 01 09 00 04 00 1D 03 20 01 00 CD
Z-Wave Debug . . sensorSetLevel: node 029, endpoint None, cmdClass 20, value 0
Z-Wave Debug filtering duplicate command -- old: 30, 0, 0, new: 20, 0, 0 (0.3242 secs)
Z-Wave Debug terminatingSyncUI

18 Mar 2016 09:28:29
Z-Wave Debug SENT setMultiLevelValue: 01 0A 00 13 14 03 26 01 FF 05 36 1A
Z-Wave Debug RCVD setMultiLevelValue: 01 05 00 13 36 01 DE (node NAK)
Z-Wave Error send "Back door light - Micro Smart Energy Illuminator (DSC19)" on failed

Posted on
Sat Mar 19, 2016 10:39 am
matt (support) offline
Site Admin
User avatar
Posts: 21411
Joined: Jan 27, 2003
Location: Texas

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

That is really odd. It looks like all the commands sent during the sync process work fine, but the commands to control always fail with a NAK.

Try excluding the module from the Z-Stick, then re-including it. Re-sync it after you are done (make sure you choose the new node ID if it changes). Does it then work?

Image

Posted on
Mon Apr 04, 2016 1:09 am
moyse offline
Posts: 39
Joined: Apr 14, 2014

Re: Aeotec Micro Smart Energy Illuminator (DSC19103)

Hi matt,

Sorry for the delay in replying - my old mac mini finally decided to die and it took me a while to get up and running again.

I exluded/included the module and it worked again ... for a day. I've ordered a replacement. I really don't seem to have a lot of luck with the reliability of my devices (though actually this was a couple of years old I guess).

Thanks for the help!