AeonLabsHEM [Update] Still doesn't appear to work in 7.1
Mon Nov 14, 2016 7:27 pm
GlennNZ offline
[/b]Hi all
Well done on i7 - I'm sure you are both relieved to have it out the door.
I have a Aeon G2 3-Phase Energy Monitoring running within Indigo 7 (Device DSB28) and for the most part seems to be working well.
I have recently had solar added to the main lines - which I believe returns power down each phase. This appears to mean the monitoring on the line is wrong.
After some research I find that I can configure the HEM by changing parameter 2 to report negative numbers (power exported I believe)
quote here:
"the HEM is configurable to show negative numbers as they do appear. You will need to set parameter 2 [1 byte dec] to 1. By default, this is set to 0 which reports the absolute value instead."
I have yet to see negative numbers in the Clamp1, Clamp2, Clamp3 Indigo devices however?
Is or will Indigo report negative Watts in these power monitoring devices?
& I am getting a
power load value out-of-bounds --2144810.743(ignored) - in the log for each clamp indicating that obviously not able to deal with negatives and some error conversion as they are all the same?
Any chance to ultimately look at this? Thanks.
Edit:
Looks like Matt made a change here in the device to ignore negatives?
Seems more to it that just ignoring as the values (-2144810.743 for all three clamps clearly are incorrect)
viewtopic.php?f=42&t=11921#p80172
Glenn
Mon Nov 14, 2016 9:07 pm
Re: AeonLabs HEM G2 3 Phase Energy Clamp - Negative W Export
The logic to decode negative incoming values is in Indigo, but it does currently drop (ignore) negative power load values because we've had experiences in the past where the meters return bogus negative values.
Regardless of that though, something else is wrong as the value being reported is way too large. Do the values always report such large negative numbers in these cases?
Mon Nov 14, 2016 9:44 pm
GlennNZ offline
Thanks for reply Matt.
Essentially once changed parameter 2 (to report negative values)
Every Clamp (which is exporting - and should be negative) is saying: (when checked every 10 minutes)
"received "Whole House - 35 - Clamp 3" power load value out-of-bounds -2144119.515W (ignored)"
Error repeats three times for all three clamps.
I agree something is up with the value?
The positive clamps which are importing/ drawing power correctly report a normal positive number.
I presume once is dark - and I'm not longer exporting any power - all clamps will report again correctly.
Is something up with handling of negative values ?
Glenn
Mon Nov 14, 2016 10:37 pm
Bollar offline
I'm curious to know if you turn the clamps around, is the number positive?
Mon Nov 14, 2016 11:25 pm
GlennNZ offline
To answer the question - if I turn them around and are exporting power - yes then the number becomes positive. But they are the correct way around for measuring incoming power.
The issue comes because power is now going in both directions; and by changing parameter one we should get negative readings (negative means power being exported, postive power being imported)
Matt
Have attached Z-Wave debug - so you can see raw value that is given to see where the -2144394.433 W comes from.
2016-11-15 16:15:16.382   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 16 0E 32 02 21 64 00 00 05 BB 02 58 00 00 05 BB D8
2016-11-15 16:15:16.384   Z-Wave Debug   . .  requestMeterLevel: node 022, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:16.385   Z-Wave Debug   . .  requestMeterLevel: 1.467 kWh (float: 1.467000)
2016-11-15 16:15:16.629   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 0E 0E 32 02 21 64 00 00 04 C2 02 58 00 00 04 C2 C0
2016-11-15 16:15:16.630   Z-Wave Debug   . .  requestMeterLevel: node 014, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:16.631   Z-Wave Debug   . .  requestMeterLevel: 1.218 kWh (float: 1.218000)
2016-11-15 16:15:16.807   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 15 0E 32 02 21 64 00 00 85 B0 02 58 00 00 85 B0 DB
2016-11-15 16:15:16.810   Z-Wave Debug   . .  requestMeterLevel: node 021, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:16.811   Z-Wave Debug   . .  requestMeterLevel: 34.224 kWh (float: 34.224000)
2016-11-15 16:15:16.813   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 4E 0E 32 02 21 64 00 00 03 D6 02 58 00 00 03 D6 80
2016-11-15 16:15:16.814   Z-Wave Debug   . .  requestMeterLevel: node 078, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:16.815   Z-Wave Debug   . .  requestMeterLevel: 0.982 kWh (float: 0.982000)
2016-11-15 16:15:16.887   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 12 0E 32 02 21 64 00 00 43 BB 01 09 00 00 43 BB 8E
2016-11-15 16:15:16.889   Z-Wave Debug   . .  requestMeterLevel: node 018, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:16.891   Z-Wave Debug   . .  requestMeterLevel: 17.339 kWh (float: 17.339000)
2016-11-15 16:15:16.967   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 0D 0E 32 02 21 64 00 00 48 22 02 58 00 00 48 22 C3
2016-11-15 16:15:16.969   Z-Wave Debug   . .  requestMeterLevel: node 013, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:16.970   Z-Wave Debug   . .  requestMeterLevel: 18.466 kWh (float: 18.466000)
2016-11-15 16:15:17.048   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 13 0E 32 02 21 64 00 02 4E 17 02 58 00 02 4E 17 DD
2016-11-15 16:15:17.050   Z-Wave Debug   . .  requestMeterLevel: node 019, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:17.050   Z-Wave Debug   . .  requestMeterLevel: 151.063 kWh (float: 151.063000)
2016-11-15 16:15:17.084   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 17 0E 32 02 21 64 00 00 F6 17 02 58 00 00 F6 17 D9
2016-11-15 16:15:17.085   Z-Wave Debug   . .  requestMeterLevel: node 023, endpoint None, meterType 01, raw value 6400...
2016-11-15 16:15:17.086   Z-Wave Debug   . .  requestMeterLevel: 62.999 kWh (float: 62.999000)
2016-11-15 16:15:20.336   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 08 28 0E 32 02 21 74 00 80 4E F0 00 00 2E BA 02 58 54
2016-11-15 16:15:20.338   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint None, meterType 01, raw value 7400...
2016-11-15 16:15:20.340   Z-Wave Debug   . .  requestMeterLevel: 8408.816 W (float: 8408.816000)
2016-11-15 16:15:20.342   Z-Wave   received "Whole House - Meter Total" power load to 8408.816 W
2016-11-15 16:15:20.359   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 28 0E 32 02 21 74 00 80 4E F0 00 00 2E BA 02 58 5C
2016-11-15 16:15:20.361   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint None, meterType 01, raw value 7400...
2016-11-15 16:15:20.362   Z-Wave Debug   . .  requestMeterLevel: 8408.816 W (float: 8408.816000)
2016-11-15 16:15:20.483   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 08 28 0E 32 02 21 64 01 EA 48 FB 02 58 01 EA 43 A1 BF
2016-11-15 16:15:20.485   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint None, meterType 01, raw value 6401...
2016-11-15 16:15:20.486   Z-Wave Debug   . .  requestMeterLevel: 32131.323 kWh (float: 32131.323000)
2016-11-15 16:15:20.488   Z-Wave   received "Whole House - Meter Total" energy total to 32131.323 kWh
2016-11-15 16:15:20.552   Z-Wave Debug   RCVD requestMeterLevel: 01 14 00 04 00 28 0E 32 02 21 64 01 EA 48 FB 02 58 01 EA 43 A1 B7
2016-11-15 16:15:20.554   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint None, meterType 01, raw value 6401...
2016-11-15 16:15:20.556   Z-Wave Debug   . .  requestMeterLevel: 32131.323 kWh (float: 32131.323000)
2016-11-15 16:15:20.695   Z-Wave Debug   RCVD multiEndPointPacket: 01 12 00 04 08 28 0C 60 0D 01 00 32 02 21 74 80 2F 23 3F 7F
2016-11-15 16:15:20.697   Z-Wave Debug   . .  multiEndPointPacket: node 040, endPoint 1
2016-11-15 16:15:20.698   Z-Wave Debug   RCVD requestMeterLevel: 01 0E 00 04 08 28 08 32 02 21 74 80 2F 23 3F FF
2016-11-15 16:15:20.700   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint 1, meterType 01, raw value 7480...
2016-11-15 16:15:20.700   Z-Wave Debug   . .  requestMeterLevel: -2144394.433 W (float: -2144394.433000)
2016-11-15 16:15:20.701   Z-Wave   received "Whole House - 35 - Clamp 1" power load to -2144394.433 W
2016-11-15 16:15:20.702   Z-Wave Error   received "Whole House - 35 - Clamp 1" power load value out-of-bounds -2144394.433 W (ignored)
2016-11-15 16:15:20.732   Z-Wave Debug   RCVD multiEndPointPacket: 01 12 00 04 00 28 0C 60 0D 01 00 32 02 21 74 80 2F 23 3F 77
2016-11-15 16:15:20.734   Z-Wave Debug   . .  multiEndPointPacket: node 040, endPoint 1
2016-11-15 16:15:20.736   Z-Wave Debug   RCVD requestMeterLevel: 01 0E 00 04 00 28 08 32 02 21 74 80 2F 23 3F FF
2016-11-15 16:15:20.737   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint 1, meterType 01, raw value 7480...
2016-11-15 16:15:20.739   Z-Wave Debug   . .  requestMeterLevel: -2144394.433 W (float: -2144394.433000)
2016-11-15 16:15:20.739   Z-Wave   received "Whole House - 35 - Clamp 1" power load to -2144394.433 W
2016-11-15 16:15:20.741   Z-Wave Error   received "Whole House - 35 - Clamp 1" power load value out-of-bounds -2144394.433 W (ignored)
2016-11-15 16:15:20.921   Z-Wave Debug   RCVD multiEndPointPacket: 01 12 00 04 08 28 0C 60 0D 02 00 32 02 21 74 80 20 76 7A 63
2016-11-15 16:15:20.923   Z-Wave Debug   . .  multiEndPointPacket: node 040, endPoint 2
2016-11-15 16:15:20.925   Z-Wave Debug   RCVD requestMeterLevel: 01 0E 00 04 08 28 08 32 02 21 74 80 20 76 7A FF
2016-11-15 16:15:20.926   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint 2, meterType 01, raw value 7480...
2016-11-15 16:15:20.928   Z-Wave Debug   . .  requestMeterLevel: -2145356.166 W (float: -2145356.166000)
2016-11-15 16:15:20.928   Z-Wave   received "Whole House - 035 - Clamp 2" power load to -2145356.166 W
2016-11-15 16:15:20.929   Z-Wave Error   received "Whole House - 035 - Clamp 2" power load value out-of-bounds -2145356.166 W (ignored)
2016-11-15 16:15:20.930   Z-Wave Debug   RCVD multiEndPointPacket: 01 12 00 04 00 28 0C 60 0D 02 00 32 02 21 74 80 20 76 7A 6B
2016-11-15 16:15:20.930   Z-Wave Debug   . .  multiEndPointPacket: node 040, endPoint 2
2016-11-15 16:15:20.931   Z-Wave Debug   RCVD requestMeterLevel: 01 0E 00 04 00 28 08 32 02 21 74 80 20 76 7A FF
2016-11-15 16:15:20.932   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint 2, meterType 01, raw value 7480...
2016-11-15 16:15:20.932   Z-Wave Debug   . .  requestMeterLevel: -2145356.166 W (float: -2145356.166000)
2016-11-15 16:15:20.933   Z-Wave   received "Whole House - 035 - Clamp 2" power load to -2145356.166 W
2016-11-15 16:15:20.934   Z-Wave Error   received "Whole House - 035 - Clamp 2" power load value out-of-bounds -2145356.166 W (ignored)
2016-11-15 16:15:21.104   Z-Wave Debug   RCVD multiEndPointPacket: 01 12 00 04 08 28 0C 60 0D 03 00 32 02 21 74 80 30 B5 37 FC
2016-11-15 16:15:21.107   Z-Wave Debug   . .  multiEndPointPacket: node 040, endPoint 3
2016-11-15 16:15:21.108   Z-Wave Debug   RCVD requestMeterLevel: 01 0E 00 04 08 28 08 32 02 21 74 80 30 B5 37 FF
2016-11-15 16:15:21.110   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint 3, meterType 01, raw value 7480...
2016-11-15 16:15:21.111   Z-Wave Debug   . .  requestMeterLevel: -2144291.529 W (float: -2144291.529000)
2016-11-15 16:15:21.112   Z-Wave   received "Whole House - 035 - Clamp 3" power load to -2144291.529 W
2016-11-15 16:15:21.114   Z-Wave Error   received "Whole House - 035 - Clamp 3" power load value out-of-bounds -2144291.529 W (ignored)
2016-11-15 16:15:21.129   Z-Wave Debug   RCVD multiEndPointPacket: 01 12 00 04 00 28 0C 60 0D 03 00 32 02 21 74 80 30 B5 37 F4
2016-11-15 16:15:21.131   Z-Wave Debug   . .  multiEndPointPacket: node 040, endPoint 3
2016-11-15 16:15:21.133   Z-Wave Debug   RCVD requestMeterLevel: 01 0E 00 04 00 28 08 32 02 21 74 80 30 B5 37 FF
2016-11-15 16:15:21.134   Z-Wave Debug   . .  requestMeterLevel: node 040, endpoint 3, meterType 01, raw value 7480...
2016-11-15 16:15:21.135   Z-Wave Debug   . .  requestMeterLevel: -2144291.529 W (float: -2144291.529000)
2016-11-15 16:15:21.135   Z-Wave   received "Whole House - 035 - Clamp 3" power load to -2144291.529 W
2016-11-15 16:15:21.136   Z-Wave Error   received "Whole House - 035 - Clamp 3" power load value out-of-bounds -2144291.529 W
Sat Nov 19, 2016 12:21 am
GlennNZ offline
Hi
Hi, sort of a bump... - but any further info needed?
It seems indigo device def miss reads the negative power and gives us the -2145356.166 value ?
Any pointers and will see if I can use zwave API to create the right data - because essentially I'm not getting any usable data from indigo at the moment.
Thanks a bunch!
Glenn
Sat Nov 19, 2016 9:42 am
We will look into it, but we have a backlog of support questions and buglets we are looking into. So it may be a week or two.
A question that will help me track down the problem: what is the ballpark value that should be shown above (instead of around -214481)?
Wed Nov 23, 2016 8:25 pm
GlennNZ offline
Thanks for looking into it.
The ballpark figure would be from 0 -1000-2000W or so. :) Sorry so Ballpark!
I'm trying to capture the error (and also then manually capture the reported solar generation at same time) when only 1 clamp is negative - so then can give a pretty accurate number.
if it helps here is a Smarthings device type that supports negative/positive reporting through parameter 2
https://github.com/bridaus/Aeontec-2nd- ... gy%20Meter
Thanks.
Glenn
Tue Oct 17, 2017 11:56 pm
GlennNZ offline
Re: AeonLabs HEM Monitor - [Update] still issues in 7.1 ??
7.1 Indigo Version
Have been looking forward to negative reporting Watt support for a while (well since at least Nov 16 as above)
7.1
Modified Z-Wave power (Watts) states to allow for negative values (useful for solar/wind systems).
Pleased to see it in the 7.1 list of features -- but.. does not seem supported for me..
Upgraded to 7.1
Went well - no immediate issues
Define and Resync DSB28 Home Energy Monitor
Still same as prior errors ?
Is there something I missing?
Syncing - started for "Whole House - Meter Total"
   Z-Wave                          Syncing - retrieved module neighbors list: 2, 3, 4, 7, 10, 11, 15, 16, 29, 31, 35, 36, 39, 41, 44, 46, 48, 52, 54, 55, 56, 57, 58, 60, 69, 93, 95
   Z-Wave                          Syncing - assigning return route to "040 - Whole House - Meter Total"
   Z-Wave                          Syncing - retrieved manufacture and model names: Aeon Labs - 0086, Home Energy Monitor (DSB28) - 0002001C
   Z-Wave                          Syncing - retrieved protocol version 3.40, app version 1.02
   Z-Wave                          Syncing - retrieved class hierarchy: Routing Slave : Meter : Simple Meter (04 : 31 : 01, base 32)
   Z-Wave                          Syncing - retrieved command classes: 20v1 60v3 85v1 86v1 72v1 70v1 32v3
   Z-Wave                          Syncing - retrieved encrypt commands: - none -
   Z-Wave                          Syncing - retrieved capabilities: routing, beaming
   Z-Wave                          Syncing - retrieved multi-endpoint types: 1:(31 : 01), 2:(31 : 01), 3:(31 : 01)
   Z-Wave                          Syncing - retrieved multi-endpoint classes: 1:[32], 2:[32], 3:[32]
   Z-Wave                          Syncing - retrieved group 1 associations: [1]
   Z-Wave                          Syncing - group 1 association to interface already exists (skipping)
   Z-Wave                          Syncing - retrieved parameter 3 "Enable energy change reports" is false
   Z-Wave                          Syncing - device "040 - Whole House - Meter Total" parameter 3 "Enable energy change reports" changed to false
   Z-Wave                          Syncing - retrieved parameter 4 "Report threshold watts for total" is 50 watts
   Z-Wave                          Syncing - retrieved parameter 5 "Report threshold watts for clamp 1" is 50 watts
   Z-Wave                          Syncing - retrieved parameter 6 "Report threshold watts for clamp 2" is 50 watts
   Trigger                         Outside Temp Changed Save to File
   Action Group                    Write Outside Temp to File
   Z-Wave                          Syncing - retrieved parameter 7 "Report threshold watts for clamp 3" is 50 watts
   Z-Wave                          Syncing - retrieved parameter 8 "Report threshold percentage for total" is 10 %
   Z-Wave                          Syncing - retrieved parameter 9 "Report threshold percentage for clamp 1" is 10 %
   Z-Wave                          Syncing - retrieved parameter 10 "Report threshold percentage for clamp 2" is 10 %
   Z-Wave                          Syncing - retrieved parameter 11 "Report threshold percentage for clamp 3" is 10 %
   Z-Wave                          Syncing - retrieved parameter 111 "Reporting interval" is 600 seconds
   Z-Wave                          Syncing - retrieved parameter 112 "Reporting interval2" is 600 seconds
   Z-Wave                          Syncing - device "040 - Whole House - Meter Total" parameter 112 "Reporting interval2" changed to 600 seconds (was 600 seconds)
   Z-Wave                          Syncing - retrieved parameter 113 "Reporting interval3" is 600 seconds
   Z-Wave                          Syncing - device "040 - Whole House - Meter Total" parameter 113 "Reporting interval3" changed to 600 seconds (was 600 seconds)
   Z-Wave                          Syncing - retrieved parameter 101 "Group 1 flags" is 16131
   Z-Wave                          Syncing - device "040 - Whole House - Meter Total" parameter 101 "Group 1 flags" changed to 16131 (was 16131)
   Z-Wave                          Syncing - retrieved parameter 102 "Group 2 flags" is 0
   Z-Wave                          Syncing - device "040 - Whole House - Meter Total" parameter 102 "Group 2 flags" changed to 0
   Z-Wave                          Syncing - retrieved parameter 103 "Group 3 flags" is 0
   Z-Wave                          Syncing - device "040 - Whole House - Meter Total" parameter 103 "Group 3 flags" changed to 0
   Z-Wave                          sent "Whole House - Meter Total" energy status request
   Z-Wave                          sent "Whole House - 35 - Clamp 1" energy status request
   Z-Wave                          sent "Whole House - 035 - Clamp 2" energy status request
   Z-Wave                          sent "Whole House - 035 - Clamp 3" energy status request
   Z-Wave                          received "Whole House - 035 - Clamp 3" energy total to 14387.365 kWh
   Z-Wave                          received "Whole House - 035 - Clamp 3" power load to -2145761.716 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 3" power load value out-of-bounds -2145761.716 W (ignored)
   Z-Wave                          received "Whole House - 035 - Clamp 2" energy total to 27292.366 kWh
   Z-Wave                          received "Whole House - 035 - Clamp 2" power load to -2146639.235 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 2" power load value out-of-bounds -2146639.235 W (ignored)
   Z-Wave                          received "Whole House - 35 - Clamp 1" energy total to 19629.798 kWh
   Z-Wave                          received "Whole House - 35 - Clamp 1" power load to -2145595.565 W
   Z-Wave Error                    received "Whole House - 35 - Clamp 1" power load value out-of-bounds -2145595.565 W (ignored)
   Z-Wave                          received "Whole House - Meter Total" energy total to 61309.529 kWh
   Z-Wave                          received "Whole House - Meter Total" power load to 4540.434 W
Device Details
Indigo Z-Wave Version: 2.0.103
Node ID: 40
Model: Home Energy Monitor (DSB28)
Model ID: 0002001C
Manufacturer: Aeon Labs
Manufacturer ID: 0086
Protocol Version: 3.40
Application Version: 1.02
Model Definition Version: 3
Library Type: 3
Class Name: Simple Meter
Class Hierarchy: 04 : 31 : 01
Command Class Base: 32
Command Versions: 20v1 60v3 85v1 86v1 72v1 70v1 32v3
Multi-Endpoint Types: 1:(31 : 01), 2:(31 : 01), 3:(31 : 01)
Multi-Endpoint Classes: 1:[32], 2:[32], 3:[32]
Features: routing, beaming, energyMeter
Neighbors: 2, 3, 4, 7, 10, 11, 15, 16, 29, 31, 35, 36, 39, 41, 44, 46, 48, 52, 54, 55, 56, 57, 58, 60, 69, 93, 95
Associations: 1:[1]
Config Values: 3:0 4:50 5:50 6:50 7:50 8:10 9:10 10:10 11:10 111:600 112:600 113:600 103:0 102:0 101:16131
& Yay! for Z-wave watcher plugin - Raw Z-wave stuff
 Z-Wave                          received "Whole House - Meter Total" power load to 3876.174 W
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 74 00 3B 25 4E 00 00 03 A7 82 0C DE
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 74 00 3B 25 4E 00 00 03 A7 82 0C D6
   Z-Wave                          received "Whole House - Meter Total" energy total to 61310.175 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 64 03 A7 84 DF 01 EC 03 A7 82 59 D9
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 64 03 A7 84 DF 01 EC 03 A7 82 59 D1
   Z-Wave                          received "Whole House - 35 - Clamp 1" power load to -2145757.164 W
   Z-Wave Error                    received "Whole House - 35 - Clamp 1" power load value out-of-bounds -2145757.164 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 08 28 08 32 02 21 74 80 1A 58 14 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 01 00 32 02 21 74 80 1A 58 14 1A
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 00 28 08 32 02 21 74 80 1A 58 14 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 01 00 32 02 21 74 80 1A 58 14 12
   Z-Wave                          received "Whole House - 035 - Clamp 2" power load to -2147049.958 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 2" power load value out-of-bounds -2147049.958 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 08 28 08 32 02 21 74 80 06 9E 1A FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 02 00 32 02 21 74 80 06 9E 1A CD
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 00 28 08 32 02 21 74 80 06 9E 1A FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 02 00 32 02 21 74 80 06 9E 1A C5
   Z-Wave                          received "Whole House - 035 - Clamp 3" power load to -2145767.648 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 3" power load value out-of-bounds -2145767.648 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 08 28 08 32 02 21 74 80 1A 2F 20 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 03 00 32 02 21 74 80 1A 2F 20 5B
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 00 28 08 32 02 21 74 80 1A 2F 20 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 03 00 32 02 21 74 80 1A 2F 20 53
   Z-Wave                          received "Whole House - 35 - Clamp 1" energy total to 19630.070 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 08 28 0E 32 02 21 64 01 2B 87 F6 01 EC 01 2B 86 E6 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 01 00 32 02 21 64 01 2B 87 F6 01 EC 01 2B 86 E6 34
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 00 28 0E 32 02 21 64 01 2B 87 F6 01 EC 01 2B 86 E6 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 01 00 32 02 21 64 01 2B 87 F6 01 EC 01 2B 86 E6 3C
   Z-Wave                          received "Whole House - 035 - Clamp 2" energy total to 27292.472 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 08 28 0E 32 02 21 64 01 A0 73 38 01 ED 01 A0 72 CE FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 02 00 32 02 21 64 01 A0 73 38 01 ED 01 A0 72 CE D0
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 00 28 0E 32 02 21 64 01 A0 73 38 01 ED 01 A0 72 CE FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 02 00 32 02 21 64 01 A0 73 38 01 ED 01 A0 72 CE D8
   Z-Wave                          received "Whole House - 035 - Clamp 3" energy total to 14387.633 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 08 28 0E 32 02 21 64 00 DB 89 B1 01 ED 00 DB 88 A5 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 03 00 32 02 21 64 00 DB 89 B1 01 ED 00 DB 88 A5 33
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 00 28 0E 32 02 21 64 00 DB 89 B1 01 ED 00 DB 88 A5 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 03 00 32 02 21 64 00 DB 89 B1 01 ED 00 DB 88 A5 3B
Total Power across all clamps at the time of this recording is close to negative 3113 W.
   Z-Wave                          received "Whole House - Meter Total" power load to 3536.629 W
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 74 00 35 F6 F5 00 00 89 B1 01 ED 46
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 74 00 35 F6 F5 00 00 89 B1 01 ED 4E
   Z-Wave                          received "Whole House - Meter Total" energy total to 61310.788 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 64 03 A7 87 44 02 58 03 A7 84 DF 76
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 64 03 A7 87 44 02 58 03 A7 84 DF 7E
   Z-Wave                          received "Whole House - 35 - Clamp 1" power load to -2145914.004 W
   Z-Wave Error                    received "Whole House - 35 - Clamp 1" power load value out-of-bounds -2145914.004 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 08 28 08 32 02 21 74 80 17 F3 6C FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 01 00 32 02 21 74 80 17 F3 6C C4
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 00 28 08 32 02 21 74 80 17 F3 6C FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 01 00 32 02 21 74 80 17 F3 6C CC
   Z-Wave                          received "Whole House - 035 - Clamp 2" power load to -2147082.513 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 2" power load value out-of-bounds -2147082.513 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 08 28 08 32 02 21 74 80 06 1E EF FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 02 00 32 02 21 74 80 06 1E EF B8
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 00 28 08 32 02 21 74 80 06 1E EF FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 02 00 32 02 21 74 80 06 1E EF B0
   Z-Wave                          received "Whole House - 035 - Clamp 3" power load to -2145917.798 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 3" power load value out-of-bounds -2145917.798 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 08 28 08 32 02 21 74 80 17 E4 9A FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 03 00 32 02 21 74 80 17 E4 9A 27
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 00 28 08 32 02 21 74 80 17 E4 9A FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 03 00 32 02 21 74 80 17 E4 9A 2F
   Z-Wave                          received "Whole House - 35 - Clamp 1" energy total to 19630.343 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 08 28 0E 32 02 21 64 01 2B 89 07 02 58 01 2B 87 F6 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 01 00 32 02 21 64 01 2B 89 07 02 58 01 2B 87 F6 6D
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 00 28 0E 32 02 21 64 01 2B 89 07 02 58 01 2B 87 F6 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 01 00 32 02 21 64 01 2B 89 07 02 58 01 2B 87 F6 65
   Z-Wave                          received "Whole House - 035 - Clamp 2" energy total to 27292.546 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 08 28 0E 32 02 21 64 01 A0 73 82 02 58 01 A0 73 38 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 02 00 32 02 21 64 01 A0 73 82 02 58 01 A0 73 38 2B
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 00 28 0E 32 02 21 64 01 A0 73 82 02 58 01 A0 73 38 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 02 00 32 02 21 64 01 A0 73 82 02 58 01 A0 73 38 23
   Z-Wave                          received "Whole House - 035 - Clamp 3" energy total to 14387.899 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 08 28 0E 32 02 21 64 00 DB 8A BB 02 58 00 DB 89 B1 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 03 00 32 02 21 64 00 DB 8A BB 02 58 00 DB 89 B1 99
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 00 28 0E 32 02 21 64 00 DB 8A BB 02 58 00 DB 89 B1 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 03 00 32 02 21 64 00 DB 8A BB 02 58 00 DB 89 B1 91
   Z-Wave                          received "Whole House - Meter Total" power load to 3130.321 W
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 74 00 2F C3 D1 00 00 8A BB 02 58 F2
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 74 00 2F C3 D1 00 00 8A BB 02 58 FA
   Z-Wave                          received "Whole House - Meter Total" energy total to 61311.328 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 64 03 A7 89 60 02 58 03 A7 87 44 C4
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 64 03 A7 89 60 02 58 03 A7 87 44 CC
   Z-Wave                          received "Whole House - 35 - Clamp 1" power load to -2146093.191 W
   Z-Wave Error                    received "Whole House - 35 - Clamp 1" power load value out-of-bounds -2146093.191 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 08 28 08 32 02 21 74 80 15 37 79 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 01 00 32 02 21 74 80 15 37 79 17
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 00 28 08 32 02 21 74 80 15 37 79 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 01 00 32 02 21 74 80 15 37 79 1F
   Z-Wave                          received "Whole House - 035 - Clamp 2" power load to -2147109.342 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 2" power load value out-of-bounds -2147109.342 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 08 28 08 32 02 21 74 80 05 B6 22 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 02 00 32 02 21 74 80 05 B6 22 DE
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 00 28 08 32 02 21 74 80 05 B6 22 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 02 00 32 02 21 74 80 05 B6 22 D6
   Z-Wave                          received "Whole House - 035 - Clamp 3" power load to -2146118.090 W
   Z-Wave Error                    received "Whole House - 035 - Clamp 3" power load value out-of-bounds -2146118.090 W (ignored)
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 08 28 08 32 02 21 74 80 14 D6 36 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 03 00 32 02 21 74 80 14 D6 36 BA
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 00 28 08 32 02 21 74 80 14 D6 36 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 03 00 32 02 21 74 80 14 D6 36 B2
   Z-Wave                          received "Whole House - 35 - Clamp 1" energy total to 19630.583 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 08 28 0E 32 02 21 64 01 2B 89 F7 02 58 01 2B 89 07 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 01 00 32 02 21 64 01 2B 89 F7 02 58 01 2B 89 07 62
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 00 28 0E 32 02 21 64 01 2B 89 F7 02 58 01 2B 89 07 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 01 00 32 02 21 64 01 2B 89 F7 02 58 01 2B 89 07 6A
   Z-Wave                          received "Whole House - 035 - Clamp 2" energy total to 27292.610 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 08 28 0E 32 02 21 64 01 A0 73 C2 02 58 01 A0 73 82 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 02 00 32 02 21 64 01 A0 73 C2 02 58 01 A0 73 82 D1
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 00 28 0E 32 02 21 64 01 A0 73 C2 02 58 01 A0 73 82 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 02 00 32 02 21 64 01 A0 73 C2 02 58 01 A0 73 82 D9
   Z-Wave                          received "Whole House - 035 - Clamp 3" energy total to 14388.135 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 08 28 0E 32 02 21 64 00 DB 8B A7 02 58 00 DB 8A BB FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 03 00 32 02 21 64 00 DB 8B A7 02 58 00 DB 8A BB 8D
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 00 28 0E 32 02 21 64 00 DB 8B A7 02 58 00 DB 8A BB FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 03 00 32 02 21 64 00 DB 8B A7 02 58 00 DB 8A BB 85
   Z-Wave                          received "(U) MainBathroom -  - Luminance" sensor update to 1402 lux
-------------------------------- No longer any negative values as not generating enough power ----------------- so no errors --------------------------------------------------
   Z-Wave                          received "Whole House - Meter Total" power load to 1171.266 W
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 74 00 11 DF 42 00 00 8C 69 02 58 97
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 74 00 11 DF 42 00 00 8C 69 02 58 9F
   Z-Wave                          received "Whole House - Meter Total" energy total to 61311.980 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 08 28 0E 32 02 21 64 03 A7 8B EC 02 58 03 A7 8B 0C 0E
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 14 00 04 00 28 0E 32 02 21 64 03 A7 8B EC 02 58 03 A7 8B 0C 06
   Z-Wave                          received "Whole House - 35 - Clamp 1" power load to 35.106 W
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 08 28 08 32 02 21 74 00 00 89 22 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 01 00 32 02 21 74 00 00 89 22 67
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 0E 00 04 00 28 08 32 02 21 74 00 00 89 22 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 01 00 32 02 21 74 00 00 89 22 6F
   Z-Wave                          received "Whole House - 035 - Clamp 2" power load to 1005.736 W
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 08 28 08 32 02 21 74 00 0F 58 A8 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 02 00 32 02 21 74 00 0F 58 A8 30
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 0E 00 04 00 28 08 32 02 21 74 00 0F 58 A8 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 02 00 32 02 21 74 00 0F 58 A8 38
   Z-Wave                          received "Whole House - 035 - Clamp 3" power load to 130.424 W
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 08 28 08 32 02 21 74 00 01 FD 78 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 08 28 0C 60 0D 03 00 32 02 21 74 00 01 FD 78 4A
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 0E 00 04 00 28 08 32 02 21 74 00 01 FD 78 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 12 00 04 00 28 0C 60 0D 03 00 32 02 21 74 00 01 FD 78 42
   Z-Wave                          received "Whole House - 35 - Clamp 1" energy total to 19630.811 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 08 28 0E 32 02 21 64 01 2B 8A DB 02 58 01 2B 8A C1 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 01 00 32 02 21 64 01 2B 8A DB 02 58 01 2B 8A C1 88
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 1): 01 14 00 04 00 28 0E 32 02 21 64 01 2B 8A DB 02 58 01 2B 8A C1 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 01 00 32 02 21 64 01 2B 8A DB 02 58 01 2B 8A C1 80
   Z-Wave                          received "Whole House - 035 - Clamp 2" energy total to 27292.811 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 08 28 0E 32 02 21 64 01 A0 74 8B 02 58 01 A0 73 E2 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 02 00 32 02 21 64 01 A0 74 8B 02 58 01 A0 73 E2 FF
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 2): 01 14 00 04 00 28 0E 32 02 21 64 01 A0 74 8B 02 58 01 A0 73 E2 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 02 00 32 02 21 64 01 A0 74 8B 02 58 01 A0 73 E2 F7
   Z-Wave                          received "Whole House - 035 - Clamp 3" energy total to 14388.358 kWh
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 08 28 0E 32 02 21 64 00 DB 8C 86 02 58 00 DB 8C 69 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 08 28 12 60 0D 03 00 32 02 21 64 00 DB 8C 86 02 58 00 DB 8C 69 7F
   Z-Wave Watcher Debug            Raw command received (Node 40 Endpoint 3): 01 14 00 04 00 28 0E 32 02 21 64 00 DB 8C 86 02 58 00 DB 8C 69 FF
   Z-Wave Watcher Debug            Raw command received (Node 40): 01 18 00 04 00 28 12 60 0D 03 00 32 02 21 64 00 DB 8C 86 02 58 00 DB 8C 69 77
Wed Oct 18, 2017 1:12 am
CrazyFin offline
Re: AeonLabsHEM [Update] Still doesn't appear to work in 7.1
@GlennNZ:
Can you check under "Edit Device" and check what firmware version you see the there?
I see in your device log that you have "Application version 1.02" which would implicate firmware version 1.02 but I have only seen firmware versions 1.05, 1.07 and 1.08. I have one unit with 1.05 and another one with 1.08.
If you do have firmware 1.02 then it is definately a very old firmware version.
I have been in contact with Aeotec about difference between 1.05 and 1.08 and they had no release notes to offer me but they said the following about 1.07:
"The HEM G2 units logs had an issue in the past with V1.07 outputting 3x the amount of kwh which is the change from V1.07 to V1.08."
You can contact Aeotec support and create a support ticket at https://aeotec.freshdesk.com/support/home
Can you check the EXACT model number you have by looking at Aeotecs / Aeon Labs model number definitions on this link: https://aeotec.freshdesk.com/support/solutions/articles/6000027557-what-are-aeon-labs-product-codes-
Wed Oct 18, 2017 1:26 am
GlennNZ offline
Yep its firmware 1.02 (*well that is what is reported)
Not sure this is a firmware issue - as reports positives fine - just negatives having same errors as always despite moving up to 7.1
Glenn
Wed Oct 18, 2017 1:29 am
CrazyFin offline
Ok cool but I would still create a support ticket with Aeotec and ask them if firmware 1.02 has issues with negative power reports since the lowest official firmware version I have seen for the DBS28 units is 1.05.
Wed Oct 18, 2017 1:46 am
GlennNZ offline
Maybe.
But - Is anyone having negative reports on other firmware?
It’s behaving as I would expect - except that when negative reporting is on indigo errors out as above. I can’t find it now but the difference of firmware versions was pretty minimal I seem to recall.
Glenn
Wed Oct 18, 2017 2:39 am
CrazyFin offline
Ok looking at for example these lines in your debug logs:
The sequences of "74 00 11 DF 42" and "74 00 35 F6 F5 00" are where the value of the load comes in. If I have understood it correctly the "74 00" packet indicates that the numbers that follows is the power load.
"64 00" would indicate energy number. I am not 100% sure of this but when I was digging into my DSB28-logs for other reasons that was the pattern I saw.
So after "74 00" you get the actual power load number which in your case above is "11 DF 42" which is 1171266 in decimal form which corresponds to the 1171..266W reading you see in clear text.
The value "35 F6 F5" on the second log output equals to 3536629 that corresponds to the 3536.629W reading you see.
Ok, so for positive load on clamp 1 in the example below we see the "74 00" sequence followed by "00 89 22" which translates into 35106 (i.e. 35.106W). All good so far.
BUT, for NEGATIVE load on clamp 1 in the example below we see the sequence now is "74 80" instead of "74 00" which I think indicates that the number that follows is a negative number and should therefore be treated differently. "17 F3 6C" equals to 1569644 in decimal which would indicate a negative load of -1569.644W for clamp 1. Does this sound more correct?
I am wondering if Indigo does the calculation wrong since if you take the squence "80 17 F3 6C" and convert it to decimal you get 2149053292 which would be 2149053.292W. That is not exactly the same number as Indigo is showing but quite close.
Could it be that Indigo is parsing the secuence "74 00" and "74 80" erroneously and using the "00" and "80" as a value to be included in the load number while it actually is an indicator for either positive number follows or a negative number follows?
Looking at the negative values for clamp 2 we see "06 1E EF" after "7480" which then equals to -401.135W and for clamp 3 we see "17 E4 9A" which would be -1565.850W.
The total would then be (-1569.644) + (-401.135) + (-1575.850) = -3536.629W which is a little bit lower than your expected value?
Wed Oct 18, 2017 2:14 pm
GlennNZ offline
Thanks for the detective work!
I like your explanation and I think it does fit - the amount is probably right as my figure comes from another source (obviously this one isn’t working) and is only updated every 15 minutes or so.
I think this needs Matt to comment on.....
Glenn