2413U or 2414U

PostPosted: Wed Dec 07, 2011 7:47 am
by johnpolasek
Questoin: I have an EZIO2X4 on order to go with a 0-5 v pressure sensor that I intend to use to monitor water depth in a cistern. The Indigo system that will be tied to this device is currently using a 2414U. However, when I looked at the detailed command set for the EZIIO, it appears that while the alarm trip on the 0-5 analog input is a standard length command, the actual digitized analog value is an extended command. So does this unit require a 2413U in order to get the actual pressure value like the Imeter solo does for the actual power usage? Or does Indigo (5.02 pro) even support that function?

Re: 2413U or 2414U

PostPosted: Wed Dec 07, 2011 9:00 am
by matt (support)
Indigo can read the analog values from the EZIO modules using normal (not extended) commands, so the 2414u should work fine.