Indigo controllable power strip

Posted on
Sun Oct 08, 2017 6:48 pm
FlyingDiver offline
User avatar
Posts: 7222
Joined: Jun 07, 2014
Location: Southwest Florida, USA

Re: Indigo controllable power strip

Here's some more data from another install. I have nothing in plugs 1 and 2 (unswitched). Switched 1 (plug 3) is my Cable Modem, switched 2 (plug 4) is my Router, and switched 4 (plug 6) is my Tablo:

Code: Select all
Oct 8, 2017 at 8:42:35 PM 10/8
   Z-Wave                          sent "AV Power Strip" energy usage reset
   Z-Wave                          sent "Cable Modem Switched Outlet" energy usage reset
   Z-Wave                          sent "Router Switched Outlet" energy usage reset
   Z-Wave                          sent "Tablo Switched Outlet" energy usage reset

Oct 8, 2017 at 8:43:16 PM 10/8
   Z-Wave                          sent "Tablo Switched Outlet" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 14 00 04 00 0F 0E 32 02 21 64 00 00 00 00 00 00 00 00 00 00 FF
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 18 00 04 00 0F 12 60 0D 04 01 32 02 21 64 00 00 00 00 00 00 00 00 00 00 E3
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Endpoint:  4
   Z-Wave Power Logger Debug       Socket:    6
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave                          received "Tablo Switched Outlet" power load to 8.504 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 21 38 FF
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Total Power: 8504 (850.0) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 04 01 32 02 21 74 00 00 21 38 FE
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Endpoint:  4
   Z-Wave Power Logger Debug       Socket:    6
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Power: 8504 (850.0) watts
   Z-Wave                          sent "Router Switched Outlet" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 14 00 04 00 0F 0E 32 02 21 64 00 00 00 00 00 00 00 00 00 00 FF
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 18 00 04 00 0F 12 60 0D 02 01 32 02 21 64 00 00 00 00 00 00 00 00 00 00 E5
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Endpoint:  2
   Z-Wave Power Logger Debug       Socket:    4
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 00 00 FF
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Total Power: 0 (0.0) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 02 01 32 02 21 74 00 00 00 00 E1
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Endpoint:  2
   Z-Wave Power Logger Debug       Socket:    4
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Power: 0 (0.0) watts
   Z-Wave                          sent "Cable Modem Switched Outlet" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 14 00 04 00 0F 0E 32 02 21 64 00 00 00 00 00 00 00 00 00 00 FF
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 18 00 04 00 0F 12 60 0D 01 01 32 02 21 64 00 00 00 00 00 00 00 00 00 00 E6
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Endpoint:  1
   Z-Wave Power Logger Debug       Socket:    3
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 00 00 FF
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Total Power: 0 (0.0) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 01 01 32 02 21 74 00 00 00 00 E2
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Endpoint:  1
   Z-Wave Power Logger Debug       Socket:    3
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Power: 0 (0.0) watts
   Z-Wave                          sent "AV Power Strip" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 14 00 04 00 0F 0E 32 02 21 64 00 00 00 00 00 00 00 00 00 00 9B
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    64
   Z-Wave                          received "AV Power Strip" power load to 30.411 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 76 CB 2A
   Z-Wave Power Logger Debug       Node:      15
   Z-Wave Power Logger Debug       Total:     33
   Z-Wave Power Logger Debug       Format:    74
   Z-Wave Power Logger Debug       Total Power: 30411 (3041.0) watts
Attachments
Power Logger States.png
Power Logger States.png (42.47 KiB) Viewed 3462 times

joe (aka FlyingDiver)
my plugins: http://forums.indigodomo.com/viewforum.php?f=177

Posted on
Mon Oct 09, 2017 12:13 am
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

Sorry about debug Ross; I missed copying some code from another plugin - you shouldn’t have to reload plugin! I’ll sort that.

Thanks both for log/pics. I don’t understand why they don’t tie up so I’ll have to fine tune what I do log.

The powersocket states should only ever update if there’s a Format:34 or Format:74 and vice-versa (at the moment) so either state should be 0 or there should be a log snippet for Socket: 5.

(Format is a bit mask with several valid combinations that I’ll code to support other models later)


Sent from my iPhone using Tapatalk Pro

Posted on
Mon Oct 09, 2017 1:36 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

Just uploaded 1.0.2

Posted on
Mon Oct 09, 2017 1:44 pm
FlyingDiver offline
User avatar
Posts: 7222
Joined: Jun 07, 2014
Location: Southwest Florida, USA

Re: Indigo controllable power strip

Code: Select all
   Starting plugin "Z-Wave Power Logger 1.0.2" (pid 31291)
   Z-Wave Power Logger Error       Error in plugin execution InitializeMain:

Traceback (most recent call last):
SyntaxError: ('invalid syntax', ('plugin.py', 113, 27, '\t\t\t\tif (bytes[10] == "74"): #3DP, Watts, 4bytes\n'))

   Stopping plugin "Z-Wave Power Logger 1.0.2" (pid 31291)
   Stopped plugin "Z-Wave Power Logger 1.0.2"


Please put a link for each version when you announce it so we don't have to go back through the thread looking for the original link. ;)

joe (aka FlyingDiver)
my plugins: http://forums.indigodomo.com/viewforum.php?f=177

Posted on
Mon Oct 09, 2017 1:56 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

FlyingDiver wrote:
Please put a link for each version when you announce it so we don't have to go back through the thread looking for the original link. ;)

That means me going and finding it each time :lol:

1.0.4

http://www.oakworthmethodists.org/_Indi ... Plugin.zip

Posted on
Mon Oct 09, 2017 2:19 pm
FlyingDiver offline
User avatar
Posts: 7222
Joined: Jun 07, 2014
Location: Southwest Florida, USA

Re: Indigo controllable power strip

Still not matching outlets to data right.

Code: Select all

Oct 9, 2017, 4:16:00 PM
   Z-Wave                          sent "AV Power Strip" energy status request
   Z-Wave                          received "AV Power Strip" energy total to 0.593 kWh
   Z-Wave                          received "AV Power Strip" power load to 30.200 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 75 F8 1A
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 30200 (30.2) watts
   Z-Wave                          sent "Cable Modem Switched Outlet" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 00 00 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 0 (0.0) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 01 01 32 02 21 74 00 00 00 00 E2
   Z-Wave Power Logger Debug       Endpoint:  1
   Z-Wave Power Logger Debug       Socket:    3
   Z-Wave Power Logger Debug       State:     socket3power
   Z-Wave Power Logger Debug       Power: 0 (0.0) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 18.21 watts
   Z-Wave                          sent "Router Switched Outlet" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 00 00 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 0 (0.0) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 02 01 32 02 21 74 00 00 00 00 E1
   Z-Wave Power Logger Debug       Endpoint:  2
   Z-Wave Power Logger Debug       Socket:    4
   Z-Wave Power Logger Debug       State:     socket4power
   Z-Wave Power Logger Debug       Power: 0 (0.0) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 18.21 watts
   Z-Wave                          sent "015 - Outlet 3" energy status request
   Z-Wave                          received "015 - Outlet 3" energy total to 0.187 kWh
   Z-Wave                          received "015 - Outlet 3" power load to 9.702 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 25 E6 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 9702 (9.702) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 03 01 32 02 21 74 00 00 25 E6 23
   Z-Wave Power Logger Debug       Endpoint:  3
   Z-Wave Power Logger Debug       Socket:    5
   Z-Wave Power Logger Debug       State:     socket5power
   Z-Wave Power Logger Debug       Power: 9702 (9.702) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 18.176 watts
Attachments
Screen Shot 2017-10-09 at 4.19.08 PM 10-9.png
Screen Shot 2017-10-09 at 4.19.08 PM 10-9.png (46.48 KiB) Viewed 3345 times

joe (aka FlyingDiver)
my plugins: http://forums.indigodomo.com/viewforum.php?f=177

Posted on
Mon Oct 09, 2017 3:19 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

FlyingDiver wrote:
Still not matching outlets to data right.

Are you sure?

FlyingDiver wrote:
Code: Select all
   Z-Wave                          received "015 - Outlet 3" power load to 9.702 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 03 01 32 02 21 74 00 00 25 E6 23
   Z-Wave Power Logger Debug       Endpoint:  3
   Z-Wave Power Logger Debug       Socket:    5
   Z-Wave Power Logger Debug       State:     socket5power
   Z-Wave Power Logger Debug       Power: 9702 (9.702) watts

That's Indigo ZWave reporting 9.702w on outlet 3, then my plugin reporting 9.702w on endpoint 3, socket 5.

As I understand it:
Socket 1 = Endpoint 5 = Unswitched
Socket 2 = Endpoint 6 = Unswitched
Socket 3 = Endpoint 1 = Outlet 1 (Switched)
Socket 4 = Endpoint 2 = Outlet 2 (Switched)
Socket 5 = Endpoint 3 = Outlet 3 (Switched)
Socket 6 = Endpoint 4 = Outlet 4 (Switched)

Which looks ok at a data/plugin/command level - the only thing wrong is you said there's nothing in socket 5 but the device is physically sending a power reading from it?

Peter

Posted on
Mon Oct 09, 2017 3:35 pm
FlyingDiver offline
User avatar
Posts: 7222
Joined: Jun 07, 2014
Location: Southwest Florida, USA

Re: Indigo controllable power strip

I think it's actually:

Code: Select all
Socket 1 = Endpoint 1 = Unswitched
Socket 2 = Endpoint 2 = Unswitched
Socket 3 = Endpoint 3 = Switched 1
Socket 4 = Endpoint 4 = Switched 2
Socket 5 = Endpoint 5 = Switched 3
Socket 6 = Endpoint 6 = Switched 4


So the power readings on Endpoints 1 and 2 are correct. I'm not seeing anything on Endpoint 6.

joe (aka FlyingDiver)
my plugins: http://forums.indigodomo.com/viewforum.php?f=177

Posted on
Mon Oct 09, 2017 3:45 pm
srkinard offline
Posts: 320
Joined: Apr 10, 2016
Location: Austin, Texas

Re: Indigo controllable power strip

On mine I just checked with the new plugin and physical outlet #2 is empty but socket4 is the one with no reading.
Physical socket #1 has the small load on it and that matches socket3

I'm wondering if the sockets map weird...
socket3 = Unswitched #1 = Physical #1
socket4 = Unswitched #2 = Physical #2

Sadly with servers powering too much of the house I can't easily play with them.

I just ordered another strip to experiment with using my Kill-a-watt meter and a known load...it will arrive Wed.
Try to help narrow down exactly which sockets line up with what...

Here's the log:

Code: Select all
   Action Group                    Refresh Power Strip Energy
   Z-Wave                          sent "Computer Room Strip - All Outlets" energy status request
   Z-Wave                          received "Computer Room Strip - All Outlets" energy total to 1308.930 kWh
   Z-Wave                          received "Computer Room Strip - All Outlets" power load to 854.635 W
   Z-Wave                          sent "Computer Room Strip - Outlet 1 - ESXi 02" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 49 08 32 02 21 74 00 0D 0A 6B BD
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 854635 (854.635) watts
   Z-Wave                          received "Computer Room Strip - Outlet 1 - ESXi 02" energy total to 92.826 kWh
   Z-Wave                          received "Computer Room Strip - Outlet 1 - ESXi 02" power load to 60.733 W
   Z-Wave                          sent "Computer Room Strip - Outlet 2 - ESXi 03" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 49 08 32 02 21 74 00 00 ED 3D FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 60733 (60.733) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 49 0C 60 0D 01 01 32 02 21 74 00 00 ED 3D 74
   Z-Wave Power Logger Debug       Endpoint:  1
   Z-Wave Power Logger Debug       Socket:    3
   Z-Wave Power Logger Debug       State:     socket3power
   Z-Wave Power Logger Debug       Power: 60733 (60.733) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 17120.782 watts
   Z-Wave                          sent "Computer Room Strip - Outlet 3 - Mac Pro" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 49 08 32 02 21 74 00 00 00 00 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 0 (0.0) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 49 0C 60 0D 02 01 32 02 21 74 00 00 00 00 A7
   Z-Wave Power Logger Debug       Endpoint:  2
   Z-Wave Power Logger Debug       Socket:    4
   Z-Wave Power Logger Debug       State:     socket4power
   Z-Wave Power Logger Debug       Power: 0 (0.0) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 17120.782 watts
   Z-Wave                          received "Computer Room Strip - Outlet 3 - Mac Pro" energy total to 311.168 kWh
   Z-Wave                          received "Computer Room Strip - Outlet 3 - Mac Pro" power load to 201.686 W
   Z-Wave                          sent "Computer Room Strip - Outlet 4 - 24 bay RAID" energy status request
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 49 08 32 02 21 74 00 03 13 D6 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 201686 (201.686) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 49 0C 60 0D 03 01 32 02 21 74 00 03 13 D6 60
   Z-Wave Power Logger Debug       Endpoint:  3
   Z-Wave Power Logger Debug       Socket:    5
   Z-Wave Power Logger Debug       State:     socket5power
   Z-Wave Power Logger Debug       Power: 201686 (201.686) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 17112.588 watts
   Z-Wave                          received "Computer Room Strip - Outlet 4 - 24 bay RAID" energy total to 296.164 kWh
   Z-Wave                          received "Computer Room Strip - Outlet 4 - 24 bay RAID" power load to 188.786 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 49 08 32 02 21 74 00 02 E1 72 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 188786 (188.786) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 49 0C 60 0D 04 01 32 02 21 74 00 02 E1 72 30
   Z-Wave Power Logger Debug       Endpoint:  4
   Z-Wave Power Logger Debug       Socket:    6
   Z-Wave Power Logger Debug       State:     socket6power
   Z-Wave Power Logger Debug       Power: 188786 (188.786) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 17111.271 watts


Attaching the screen of the socket readings
Attachments
Screen Shot 2017-10-09 at 4.33.07 PM.png
Screen Shot 2017-10-09 at 4.33.07 PM.png (144.46 KiB) Viewed 3336 times

Posted on
Mon Oct 09, 2017 4:26 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

FlyingDiver wrote:
I think it's actually:

Code: Select all
Socket 1 = Endpoint 1 = Unswitched
Socket 2 = Endpoint 2 = Unswitched
Socket 3 = Endpoint 3 = Switched 1
Socket 4 = Endpoint 4 = Switched 2
Socket 5 = Endpoint 5 = Switched 3
Socket 6 = Endpoint 6 = Switched 4


So the power readings on Endpoints 1 and 2 are correct. I'm not seeing anything on Endpoint 6.


Sorry, you're correct - I've just re-read Matt's post in the 2014 thread on this subject.

For on/off commands, endpoints 1-4 are the switched sockets 3-6.
For energy reporting, endpoints 1-4 are the unswitched sockets 1-2 and the first two switched sockets 3-4.

That's where all the confusion lies. I've been applying the on/off mapping where endpoints 1-4 are sockets 3-6 and thus endpoints 5-6 would (if they existed) be sockets 1-2.

I've just put 1.0.7 up at the same link... :lol:

Note there's a new Action to reset the power levels to zero which will probably be sensible before continuing.

Peter

Posted on
Mon Oct 09, 2017 5:04 pm
FlyingDiver offline
User avatar
Posts: 7222
Joined: Jun 07, 2014
Location: Southwest Florida, USA

Re: Indigo controllable power strip

Now I'm seeing power readings on 3 and 4, but nothing on 6. Does Endpoint 5 or 6 not work? Indigo doesn't see them so the plugin can't either?

joe (aka FlyingDiver)
my plugins: http://forums.indigodomo.com/viewforum.php?f=177

Posted on
Mon Oct 09, 2017 5:06 pm
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

Are you sending my Action to request them?

Indigo will never ask them cos it doesn’t know about them.


Sent from my iPhone using Tapatalk Pro

Posted on
Mon Oct 09, 2017 5:18 pm
srkinard offline
Posts: 320
Joined: Apr 10, 2016
Location: Austin, Texas

Re: Indigo controllable power strip

The numbers I get seem to line up with what's plugged in now...

I'll test once I get the new power strip on, before I put it into use...

Posted on
Tue Oct 10, 2017 12:17 am
howartp offline
Posts: 4559
Joined: Jan 09, 2014
Location: West Yorkshire, UK

Re: Indigo controllable power strip

Great.

Can you both play with the totalpower/totalpowerrep values?

TotalPowerRep gets updated whenever it receives a 'total' power report from the device whereas TotalPower is calculated from the totals of 1-8.

I don't think TotalPowerRep is accurate because whenever an endpoint report arrives, I think it also sends a false "total" report of the same endpoint value.

I've asked Jay for a subforum in my plugins area.

Peter

Posted on
Tue Oct 10, 2017 6:31 am
FlyingDiver offline
User avatar
Posts: 7222
Joined: Jun 07, 2014
Location: Southwest Florida, USA

Re: Indigo controllable power strip

State values that are getting filled in haven't changed. And I'm not sure that using your request commands actually does anything:

Code: Select all
   Action Group                    Power Strip Testing
   Z-Wave Power Logger Debug       Node: 15
   Z-Wave Power Logger             Requesting power level 1 for node 15
   Z-Wave                          sent "AV Power Strip" raw command [60 0D 01 01 32 01 0A 25]
   Z-Wave Power Logger             Requesting power level 2 for node 15
   Z-Wave                          sent "AV Power Strip" raw command [60 0D 01 02 32 01 0A 25]
   Z-Wave Power Logger             Requesting power level 3 for node 15
   Z-Wave                          sent "AV Power Strip" raw command [60 0D 01 03 32 01 0A 25]
   Z-Wave Power Logger             Requesting power level 4 for node 15
   Z-Wave                          sent "AV Power Strip" raw command [60 0D 01 04 32 01 0A 25]
   Z-Wave Power Logger             Requesting power level 5 for node 15
   Z-Wave                          sent "AV Power Strip" raw command [60 0D 01 05 32 01 0A 25]
   Z-Wave Power Logger             Requesting power level 6 for node 15
   Z-Wave                          sent "AV Power Strip" raw command [60 0D 01 06 32 01 0A 25]


The commands are getting sent, but nothing is coming back as far as I can tell. When I use the "Update" button in the Indigo device UI, I do get something back:

Code: Select all
   Z-Wave                          sent "Tablo Switched Outlet" energy status request
   Z-Wave                          received "Tablo Switched Outlet" power load to 8.468 W
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 0E 00 04 00 0F 08 32 02 21 74 00 00 21 14 FF
   Z-Wave Power Logger Debug       Endpoint:  Total
   Z-Wave Power Logger Debug       State:     totalpowerrep
   Z-Wave Power Logger Debug       Total Power Reported: 8468 (8.468) watts
   Z-Wave Power Logger Debug       -----
   Z-Wave Power Logger Debug       Energy report received:
   Z-Wave Power Logger Debug       Raw command: 01 12 00 04 00 0F 0C 60 0D 04 01 32 02 21 74 00 00 21 14 D2
   Z-Wave Power Logger Debug       Endpoint:  4
   Z-Wave Power Logger Debug       Socket:    4
   Z-Wave Power Logger Debug       State:     socket4power
   Z-Wave Power Logger Debug       Power: 8468 (8.468) watts
   Z-Wave Power Logger Debug       Total Power Calculated: 17.934 watts


In that example, I was asking for an update for switched outlet 4, but what I got back was endpoint 4 which is the second switched outlet (physical outlet 4).

There doesn't seem to be anything I can do that will get an update from switched outlet 4 (physical outlet 6, presumably endpoint 6 for energy reports).
Attachments
Screen Shot 2017-10-10 at 8.25.29 AM 10-10.png
Screen Shot 2017-10-10 at 8.25.29 AM 10-10.png (40.32 KiB) Viewed 3258 times

joe (aka FlyingDiver)
my plugins: http://forums.indigodomo.com/viewforum.php?f=177